Discuss Switching in the Industrial Electricians' Talk area at ElectriciansForums.net
i'd split them between 3 or 4 switches. not because of the load, which is only 350w, but consider inrush, and if on 1 switch, a fault anywhere will take the lot out.
Retractive switches and a couple of latching relays if they're going to be on all day :) or above couple of circuits for a bit of discrimination so you don't lose the lot.
I have fitted 20 7w aurora's on 1 circuit... never again...
on occasions it would trip the 10A MCB when initially turning them on.
the inrush on the LED's are high.
treat them like a 50w downlight..
Yeah il use 6a type c and thinking maybe 6 circuits rooughly 25 each ..
What about that gland ive only ever used 20w isit?
might need a 10A mate :)
and why dont you read on the back of the SWA pack.. it will tell you what size gland you require..
probably a BW32 or larger
COULD ANYONE SEE A PROBLEM WITH SWITCHEN 50 X7 WATT LEDS AT ONCE http://www.websparky.co.uk/acatalog/WS-inceptor.pdf
I would recommend a 6 gang Switch M8, not on one gang myelf, and have them on 3 circuits, 2 switches per circuit, I dooney like more than 8-10 lights on one switch myself and start feeling uneasy at more than 15 on a circuit, however in answering your question load wise no problem, but good practice suggests otherwise,JMO.
You mentioned a 16mm 5-core that your installing.............is this to a load centre? If your going to split em up on 6 different circuits then you gonna be using like a 18 or 24 way panel?? Presume all on the same phase.
Reply to Switching in the Industrial Electricians' Talk area at ElectriciansForums.net
Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Looking for counsel / guidance to replace an original Dayton On/off with speed control switch. I’ve checked with a couple local electrical supply...
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Hi Guys After bit of advice please.... Called back to kitchen job today, Hamilton light switch we fitted has burnt out?! Normally decent gear so...