Hi,

Can anyone clarify for me the requirements regarding either the RCD protection of tails or glanding of tails entering a metal consumer unit in a TT system. With specific forethought to the upcoming amendment enforcing all metal consumer units.

Cheers
 
There are no specific regulations,but in order to comply with general regs then either the tails will need to have earth fault protection or measure must be taken to minimise the chance of a fault to the metal case. This would mean keeping tails sheathed all the way to the terminals....tails kept as short as possible,and most importantly an insulated bush and some form of cable clamp to prevent any movement of the tails.
 
On a TT 100ma S Type RCD protecting the tails. You would need insulated enclosure though to house the S Type RCD but then you can't use plastic on new amendment....... Very good question really, Im not sure of the answer. Someone will know on here :)
 
Will ring the NICEIC techline tomorrow and see what fob offs they can spin me. Attended a freebee Hager 'technical seminar/sales pitch' tonight through my wholesaler. The speaker couldn't give a proper answer to the question. Does anyone know of a specific double insulated/reinforced insulation grade glanding system that can accomodate tails?
 
There is mention of using wiska glands for the tails to the M/C boards , I got a phone call from Citys about some new display `M/C boards with wiska glands , Newlec , thanks but no thanks was my reply ..
 
Will ring the NICEIC techline tomorrow and see what fob offs they can spin me. Attended a freebee Hager 'technical seminar/sales pitch' tonight through my wholesaler. The speaker couldn't give a proper answer to the question. Does anyone know of a specific double insulated/reinforced insulation grade glanding system that can accomodate tails?


I can tell you exactly what the niccy will say, either an upfront S type RCD (Idn rating would depend on RA) in the tails if feeding a metal board, or use an insulated gland/bush, or use a class II certified board.

If I recall you can get a class II metal clad board with a suitably insulated cableway for the tails, some manufactures might even have conversion kits available for existing boards, Schneider maybe ?
 
I'm not sure where the bit about the new amendment is relevant. If a metal board is used on a TT now the measures I stated in post 2 apply,it will be no different under the amendment.
 
or measure must be taken to minimise the chance of a fault to the metal case. This would mean keeping tails sheathed all the way to the terminals....tails kept as short as possible,and most importantly an insulated bush and some form of cable clamp to prevent any movement of the tails.

I'm not sure where the bit about the new amendment is relevant. If a metal board is used on a TT now the measures I stated in post 2 apply,it will be no different under the amendment.

It's all well and good ensuring that the tails are kept well secure, insulated and sheathed, but what about the busbar and neutral bar?

IMHO, the only two ways to ensure adequate earth fault protection of a metal DB on a TT system are to either guarantee TN values or fit an up front s-type.

Oh, and the up front s-type will have to be housed in plastic.

This reg just makes perfect sense! LOL
 
It's all well and good ensuring that the tails are kept well secure, insulated and sheathed, but what about the busbar and neutral bar?

IMHO, the only two ways to ensure adequate earth fault protection of a metal DB on a TT system are to either guarantee TN values or fit an up front s-type.

Oh, and the up front s-type will have to be housed in plastic.

This reg just makes perfect sense! LOL

Assuming the metal DB has an RCD main switch,or was a '17th' twin RCD then the busbar(s) and neutrals would be on the RCD side and the metal case would be protected from a fault via those.
I merely stated that the requirements under the new amendment for a metal DB on a TT will be no different to those that are already in place as far as I can see.
 
Assuming the metal DB has an RCD main switch,or was a '17th' twin RCD then the busbar(s) and neutrals would be on the RCD side and the metal case would be protected from a fault via those.
I merely stated that the requirements under the new amendment for a metal DB on a TT will be no different to those that are already in place as far as I can see.

And the insulated linkage between the main switch and the two RCDs? (On a 17th edition board that is)

You're right the requirements will be no different concerning the way a metal board is protected, only that we supposedly have to fit one. Boll*cks to that, I'll be fitting plastic thanks.
 
Assuming the metal DB has an RCD main switch,or was a '17th' twin RCD then the busbar(s) and neutrals would be on the RCD side and the metal case would be protected from a fault via those.
I merely stated that the requirements under the new amendment for a metal DB on a TT will be no different to those that are already in place as far as I can see.
I know what your saying - its always been an issue where M/C CUs and TT systems are concerned, I think the point is that issue becomes all the more prevalent post June 30th 2015 when we will be forced to use M/C CUs as standard. So the manufacturers are going to have to step up and make contractors aware of the options, because at the moment all I'm getting conflicting opinions. NICEIC have just said to me that the only real option/solution is using suitable class 2 glands and reducing the likely hood of fault between the tails and the metal case using cable clamps etc.
 
NICEIC have just said to me that the only real option/solution is using suitable class 2 glands and reducing the likely hood of fault between the tails and the metal case using cable clamps etc.

And they would be very very wrong!

As I said earlier the only real option of providing earth fault protection to a metal DB on a TT system where TN Ze values cannot be guaranteed is by fitting an s-type up front.
 
And they would be very very wrong!

As I said earlier the only real option of providing earth fault protection to a metal DB on a TT system where TN Ze values cannot be guaranteed is by fitting an s-type up front.
But how do you get over the fact the RCD will have to be housed in a metal enclosure?
 
I wonder what gems they are going to come up with for say corrosive atmospheres and the like where metal enclosures are a complete No, No?? Perhaps contain the metal board within a plastic enclosure???? lol!!

The IET have been led down a path that is going to come back and bite them in the arse!!.....
 
It won't, as it would be a single RCD in an enclosure it wouldn't be a distribution board, therefore it wont be subject to the requirements of that regulation.
That's interesting I didn't know that. Bit silly though because to all intents & purposes it has all the fire risks of a DB; Tail terminations carrying the installations full load, a device which incorporates mechanical and electronic components and contacts - all capable of catastrophic failure and subsequent combustion?
 
That's interesting I didn't know that. Bit silly though because to all intents & purposes it has all the fire risks of a DB; Tail terminations carrying the installations full load, a device which incorporates mechanical and electronic components and contacts - all capable of catastrophic failure and subsequent combustion?

Exactly my point lol! The regulation is a joke, hence why I'm still happy to install plastic.
 
I wonder what gems they are going to come up with for say corrosive atmospheres and the like where metal enclosures are a complete No, No?? Perhaps contain the metal board within a plastic enclosure???? lol!!

The IET have been led down a path that is going to come back and bite them in the arse!!.....

This does only apply to domestic DBs remember. I can't think off the top of my head where you might have a corrosive environment within a dwelling?
 
What do you mean by install it correctly?
CU fires are caused by 2 things. Defective materials and poor workmanship. If a metal clad CU is installed poorly then there's still plenty of plastic in there that will melt/burn/give off toxic fumes.
This utter nonsense is the powers that be trying to escape from the fact that what went around is now coming around.
 
CU fires are caused by 2 things. Defective materials and poor workmanship. If a metal clad CU is installed poorly then there's still plenty of plastic in there that will melt/burn/give off toxic fumes.
This utter nonsense is the powers that be trying to escape from the fact that what went around is now coming around.

It's in the BEAMA statement, non-combustible CUs are being introduced to prevent the spread of fire caused by poorly made terminations!!!!!!
The mind boggles.
 
It won't, as it would be a single RCD in an enclosure it wouldn't be a distribution board, therefore it wont be subject to the requirements of that regulation.

I wish, not quite though.

The reg, extends to all similar equipment, thus a KMF, a REC2 etc.

However, they don't HAVE to be steel, they just need to meet 61439-3 & shall...
(i) have their enclosure manufactured from non-combustible material,
 
I wish, not quite though.

The reg, extends to all similar equipment, thus a KMF, a REC2 etc.

And it says this where?

It only mentions distribution boards.

The intent of the regulation may extend as you say, the wording however is all that matters for compliance purposes.

If the wording truly reflected the intent, then on a TT without TN Ze values, you'd be damned if you did and damned if you didn't.

As I keep saying, the departures section of an EIC is there for good reason! :)

Plastic all the way for me. I don't care what the regs say, you won't find me connecting tails into unprotected metal boards in domestic TT systems.
 
Archy, how about rock, preferably igneous. It will melt at high enough temperatures but I don't think a house fire would generate anything high enough.
There may be weight issues for the fixings if granite CUs existed but at least they could be made to look pretty :)
 
And it says this where?

It only mentions distribution boards.

The intent of the regulation may extend as you say, the wording however is all that matters for compliance purposes.

If the wording truly reflected the intent, then on a TT without TN Ze values, you'd be damned if you did and damned if you didn't.

As I keep saying, the departures section of an EIC is there for good reason! :)

Plastic all the way for me. I don't care what the regs say, you won't find me connecting tails into metal boards unprotected in domestic TT systems.


In the BYB:

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:

  • (i) have their enclosure manufactured from non-combustible material, or
  • (ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.
NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.
NOTE 2: The implementation date for this regulation is the 1st January 2016, but does not preclude compliance with the regulation prior to that date.

BTW, direct copy from the electronic version of the BYB a few seconds ago.
You know the scope of 61439-3
I realise that there are other 61439-* standards, and you could argue that some of them apply.
Also some similar switchgear will be made to alternative -* numbers, there in lies another failing of the reg.
 
The thing that boils my wee is, once again, the assumption that somehow electricity used in a domestic environment is somehow more dangerous than that used in a commercial setting.
How many shops have you seen with plastic CUs?
A crap termination is a crap termination. It doesn't matter if the CU is made of bloody asbestos, you cannot make a silk purse out of a pig's ear. There's still going to be combustible material in there that can and will get hot and burn.
 
Archy, how about rock, preferably igneous. It will melt at high enough temperatures but I don't think a house fire would generate anything high enough.
There may be weight issues for the fixings if granite CUs existed but at least they could be made to look pretty :)

Aye, that would look nice matching my Brazillian green granite kithen worktops.
I could locate it above the hob.
 
The thing that boils my wee is, once again, the assumption that somehow electricity used in a domestic environment is somehow more dangerous than that used in a commercial setting.
How many shops have you seen with plastic CUs?
A crap termination is a crap termination. It doesn't matter if the CU is made of bloody asbestos, you cannot make a silk purse out of a pig's ear. There's still going to be combustible material in there that can and will get hot and burn.

It is all to do with rescue / escape times in domestic premises, CU's under the stairs etc.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Tails - metal board - TT system
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
45
Unsolved
--

Advert

Thread statistics

Created
spud1,
Last reply from
spud1,
Replies
45
Views
11,971

Advert

Back
Top