DomB
Hi all,
I need to get the bonding sorted on a house I'm working on. The gas bonding is OK but the water bonding is looking to be a real pain.
Would it be acceptable to sort out the gas bonding then just link a cold-water pipe to one of the gas pipes?
Thanks very much
where is the watern incommer? remmember bond has to be within 600mm of incomming or as near as possible. Its a bit of a get out if the pipe goes into a wall and you can only access it in the roof space.
have a read of 544.1.2
Then take into account the service positions,remember that a cable bonding both services needs to be unbroken
There is nothing stopping you running a 10mm^ bonding conductor from the main MET to Gas pipe and then onto the water pipe. You will though have to ensure the continuity of the condutor and therefore you should not cut the cable it should be continous.
It is better practice to run 2 conductors, also easier to terminate as you can use a compression crimp for each termintation.
Isn't the word Practicable regarding reg 544.1.2 a wonderful get out of jail card
the regs are there as a guide. if u want you can just link it from the gas bonding,,,may b using a compression crimp but personally dont like them.
in you situation i would cut the cable before it goes to gas pipe,fit an eath block terminal an enclosure with a label stating what its for, then from there link to the other pipe.
would only do this if there was absoloutley no way of running a new earth wire to water
Egg be carefull. Yes the regs are Non statutary however in the electricity at work regulations they say if you follow BS7671 then you will comply to also to the electricity at work Act H&S ect.
the main bond has to be a continuous unbroken link. Its ok to link gas and water with the same cable but it has to be continuous. Putting an earth block in and then seperate links is like supplying 2 main earth terminals and will cause confusion later and as a spark of 20 years there no way i would do it.
i agree,
the way i suggested was a bit of a bodge but if that was the only option then thats what i would do
Thanks all.
I can't really do a continuos conductor between the gas and the water bonding, in fact I'm having trouble routing a conductor to where the water comes in at all - what I was thinking of doing was to use the gas pipe as the conductor itself, i.e. bond the gas by the gas-meter and then further down the gas pipework, when it gets near the water, link the two systems with an earthing conductor (Hmm..now I don't like the sound of it myself, I think I may be starting to answer my own question...)
544.1.2 - I'm looking very hard at that word practicable...does it mean if it's gonna mess up their new kitchen's tile work then don't bother?!
Soz - ignore this reply, I thought my previous one hadn't made it up there
stoppress! The main water inlet pipe is plastic as it comes out the floor! Only the main tap and then the pipework as it goes onwards is metal..
Does this mean I don't need to bond the water at all!?
Try this
If the incoming service pipes are made of plastic, they
do not need to be main bonded.
If the incoming pipes are made of plastic, but the
pipes within the electrical installation are made of
metal, the main bonding must be carried out. The
bonding being applied on the customer side of any
meter, main stopcock or insulating insert and of
course to the metal pipes of the installation.
The connections of the bonding wired to the pipes
has to be made with a proper clamp to BS 951
complete with the label “SAFETY ELECTRICAL
CONNECTION - DO NOT REMOVE.”
If the incoming services are made of plastic and
the pipework within the building is of plastic then
no main bonding is required. If some of the
services are of metal and some are of plastic, then
those that are of metal must be main bonded.
Taking the water's bonding from a gas pipe?
DomB,
Spudnik,