D
DNS
Just to say. "I found the fault", I took note of the suggestions from this forum and yesterday I found the fault in about 20 seconds, The two incoming tails, system used to be a tt, but I had the DNO change it to TNCS with a PME. Firstly I checked all of their connections, all ok. But when I moved the Incoming live it crackled, on further Inspection I found that it was actually the cut out fuse holders male, on the suppliers side was actually loose in the carrier socket, which was actually heating up and had started to melt the tail insulation at the termination. All rectified now with a new cut out with a PME connection within the unit. Not one thats been added seperately. I can't honestly point the finger at anyone, because I had pulled the cut out fuse out at one time and put it back, so had the DNO engineer, but it's all safe now. Thanks.Any suggestions.. I was recently asked why the lights every now and again in their living room dim slightly then go back to normal several times and lights elsewhere in the property. Without seeing it for myself. I suggested a couple of maybes. Firstly check with the adjoining neighbour, see if they are getting the same problem. They are one the same supply phase. It may be that your getting slight fluctuations in voltage supply. Secondly there may be a loose connection somewhere in the lighting circuit. OR after all this rain they might have some water ingress somewhere, into a light fitting. I'm open to any other suggestions before I start checking next week.