Grr can't attach photo again. Please look up a few posts for relevant picture..any ideas greatly appreciated!!
 
This one:

kates.jpg
 
Not at all. I'm being lazy and posting from my phone. Thank you :)
I have so many computer issues here lol reckon u would have a week of work!!


but if anyone has any ideas of next step of fault finding??
 
There's only 1volt of leakage and considering all the computer equipment that's not a major worry.
The boiler can be isolated by two different breakers on two different DBs. WTF?? Boiler was installed less than 18months ago so customer was going to contact them and get them out to fix this. I'm pinning my hopes on that being the issue hahaha. Whole place needs gutting and starting fresh but customer needs a 'lottery win' for that.
 
They have kennels on the property...and a room of the house has been turned into an office for the kennels. They have workers who run that part for them.
 
There's only 1volt of leakage and considering all the computer equipment that's not a major worry.
The boiler can be isolated by two different breakers on two different DBs. WTF?? Boiler was installed less than 18months ago so customer was going to contact them and get them out to fix this. I'm pinning my hopes on that being the issue hahaha. Whole place needs gutting and starting fresh but customer needs a 'lottery win' for that.

Leakage is current Kate not voltage.............buy yourself a leakage clamp meter worth their weight in gold :)
 