hicheers, i cant seem to upload any pics, but what i'm lookin to do is put the cieling rose back again and start again; my main prob with this is reconsiling the wires in the correct terminals, i have a simple rose attached on one side is brown and the other is blue, as far as cieling wiring is concerned i have two black wires that i believe were inserted in the section on the left attached to the live; a cpc; and 4 diffarant red wires that were split between the section of the other two termanals; two of course being the swith live and the other two that has to go to the nuetral left set of termanals hope that sounds right:dizzy2:
That doesn't sound right to me, but maybe I'm reading it wrong. You should affectively have four cables, including the lamp cord. Assuming the existing cables are all old colours you would start with loop in and loop out - this is the daisy chain of supply power from one ceiling fitting to the next. So figure out which are the loop in-loop out conductors and connect the two reds to the longer of two middle terminal blocks (live), and the two blacks to the shorter of two middle terminal blocks (neutral). If this is connected correctly - and you haven't added anything else yet - all the other lights on that circuit should now work correctly - once CPCs are connected.
.The next thing to connect is the switch live which - ideally - someone will have marked by putting red (/brown) sleeving on the black - to so it's actually a live. The red goes to same terminal block as other reds, giving a live feed to the switch. The sleeved switch live back from the switch goes to the terminal block on the edge. The brown coloured cord lead goes to this. The blue coloured lead in the cord from the lamp joins the blacks on that terminal block.
All the CPCs should then by sleeved G/Y and connected to the earth block.
Don't forget to hook the two cord leads over the pegs either side of ceiling plate to support the weight of the lamp fitting and shade.
Last edited by a moderator: