My tester wont do continuity on a live source. RCD was off for all tests, Main switch off for continuity, on for voltage checks.
Went to a friends house to replace a switch. Couldn't isolate the circuit via MCBs on the CU. There were about 10 MCBs on a split board, both RCD protected. Switched off all MCBs but still couldn't isolate power. Had to use main switch.
After replacement db fitted the rcd was tripping when powered up. After investigation found a shared neutral on the stairs lighting. Was easy enough to rectify by altering wiring. What is your opinion on putting both lighting circuits on the same rcd?
Simple tests would have shown this up before the board change.
I take it by easy fix you've just shoved both circuits on the same Rcd? So the lighting circuits still have a borrowed neutral?