Hi guys, I'm doing an outdoor temp builders supply shortly. Existing house completely demolished. 1 phase U/G supply existing from pole. 2 x OMB's outside enclosure. 1 for suppliers meter and 1 for electricians equipment. As temp supply I'll treat it as a TT supply & use PME when house built. My question is.....what size RCD should I use regarding tripping current? Thanks.
 
On a big site I would agree to an extent but an existing supply being made on a house that is being rebuilt I would personally test and use the supplied earth but your call and 30ma all the way
 
Thanks for that. The reason why I asked about the tripping current was that whilst taking 2395 recently I was told that I had to use 500ma. the reason given was that it would operate a last faster than 30ma. My grey matter is now is unable to get my head round it. What do others think?
 
For a building site if you are using the 230V supply then sockets and hand held equipment <32A need a 30mA RCD.
If you have a TT system then all circuits need RCD protection and for convenience you might as well use 30mA unless there is a specific piece of hard wired equipment that cannot manage on 30mA.
You could use a 500mA RCD for the main supply but would then need 30mA RCDs afterward, so no point.
 