I have been asked to test an offpeak cdu but what am I to do with the live tests? Do I calculate using them using ze from on peak cdu? Or do I go back at night!? Lol. Also what about schedule of inspection for functional tests??? Cheers
 
you hang around till the power comes on at 12am!!!

alternatively you LIM the live tests and calculate ZS from R1R2 + ZE (main incomer on live side)

you also LIM the functionaal tests or you disconnect and put you continuity meter either side of the switch!!
 
Yes, you do as Durham suggests or you energise (safely) the off-peak board from the 24-hour supply for the purpose of live testing.

If this is a periodic inspection then I'd go with Durham, initial verification and I just have to see everything working!
 
Firstly. Yes it is pir, confusion set in because client had spark who refused to test that board because of the off peak nature!

Secondly. Thanks for that, never thought of doing functional test like that on a storage. Won't the element just give continuity thow ????
 
Firstly. Yes it is pir, confusion set in because client had spark who refused to test that board because of the off peak nature!

Secondly. Thanks for that, never thought of doing functional test like that on a storage. Won't the element just give continuity thow ????

You will get a resistance reading through the element(s) but you'll also be able to check the switching of the input thermostat controls.(assuming storage heating)
 
Last edited:
Cheers guys, I think in order to energise it would involve breaking seal on storm fuse because there is no isolator!? I know what u mean though about seeing everything working. I got to say this forum is the best thing since sliced bread, I am getting loads of answers! Once again many thanks chaps
 
Cheers guys, I think in order to energise it would involve breaking seal on storm fuse because there is no isolator!? I know what u mean though about seeing everything working. I got to say this forum is the best thing since sliced bread, I am getting loads of answers! Once again many thanks chaps

It is a great forum, don't forget the 'thanks button' ;)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
testing off peak consumer unit
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
james86,
Last reply from
IQ Electrical,
Replies
7
Views
4,810

Advert

Back
Top