but 434.2 applies. the cable size is reduced from the tails size ( 16mm?) to the 6mm or 10mm of the shower circuit, so IMO that 6mm ( or 10mm ) should be protected with a suitable overload device. also, if the tails are henley blocked before the main CU, then any fault current is on the DNO fuse.
It's that IQ mate .....................always stirring things like you can't export a PME earth:devilish:
cpc not earthed. broken connection somewhere. do a R1+R2.
IMO "export " is a bad term. to export something means moving it from 1 place to another, when you are not doing that, you are extending it.