Good morning.

Fitted a texecom premie4 elite 64W over the weekend.
Only one problem and that is I have a EXP 1,1 Tamper fault that I am unable to clear.
Looking on various sites it points towards the commissioning jumper still being in the commissioning position.
Checked this and the jumper is in the correct position left and centre.

Any suggestions?

I have emailed Texecom the same question but just trying to clear up ASAP and move on.
 
I would loop out all tamper circuits at the panel, reset panel and if fault is clear then add one circuit at a time until you find the fault.
 
  • Like
Reactions: DPG and Spoon
i always suspect the back tamper of the external siren. esp.if the wall is a bit uneven.
 
  • Agree
Reactions: DPG and James
Thanks for the suggestions.
Tried both but it’s neither of them.
 
get meter on d.c. volts. + probe to bell +. - probe to 0V should read 13V. and - probe to tamper return also 13V.
 
If I recall correctly jumper on jp7 - left and center is commissioning mode. Remove it completely or put it right and center
 
  • Like
Reactions: Gnasher
Like this ?

TXCom JP7.PNG
 
  • Like
Reactions: Gnasher
Gentlemen you have cracked it.
I think it’s time for new glasses

The jumper was on left and centre not right and centre.

Thanks again from a grateful Sparky.
 
  • Like
  • Friendly
Reactions: DPG and James

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Texecom Premier Elite. EXP 1,1 tamper fault.
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Gnasher,
Last reply from
Gnasher,
Replies
7
Views
19,406

Advert