Nothing it would function assuming a neutral is present. Bit like connecting a single phase circuit from a triple pole board. Why you think these things.
 
Last edited:
The problem is you have the obvious issue of been able to partly energise 3ph equipment by plugging in a 3ph item to a socket with only 1ph present which should not be the case, with respect to the 1ph outlet from a 3ph/N supply then you can only plug in the correct item that requires 1ph. Also unless you single phase all the 3ph pins, you would need to ensure any plug is matched to the live pin but from my first point, you shouldn't be rigging this setup up anyway but having said that, it does go on in the land of the cowboy sparks.
 
True @spary but 2ph welders don't require correct the phone rotation so you cannot really get it wrong picking any 2 phase pins on the welder plug.:)
 
I can't see the problem, if the 3 ph socket is wired correctly using all 3 supply phases + N?
your appliance might only need 240v but uses a 5 pin plug ???
you can plug any appliance in that fits, whether it needs 1,2 or 3 phases
 
The OP was talking about a 3ph plug onto a single phase supply and that is what I was relating to, of course if you have a plug with 3ph and N then no issue if using only a few phases.
 
The most important thing here is that the socket is wired correcty. I see absolutely no problem connecting a single phase appliance through a triple pole plug.
 
I agree, no problem in supplying a single phase 230V appliance from a (five pin) red TPN plug/socket, using any one phase and the neutral.
Unwieldy and potentially confusing perhaps, but electrically OK.
But remember it will be protected somewhere by a three-pole breaker (which may not be RCD-protected), so a fault on the single-phase appliance will trip all the phases.
I say 'So what?', but when I suggested an equivalent install on one circuit in my new workshop (to get around a cable limitation), I got a load of nay-saying and abuse. But, perhaps significantly, I'm still waiting to hear why this is not acceptable.
One three-phase breaker, supplying multiple single-phase loads. OK or not? - http://www.electriciansforums.co.uk/threads/one-three-phase-breaker-supplying-multiple-single-phase-loads-ok-or-not.111198/
 
I think it is because it is unconventional but good point about the rcd, didn't occur to me.
 