So, Who ..got the solution?

:gunsmilie:Man Fights Goose, With Lightsaber - YouTube

PP3.jpg
 
Last edited by a moderator:
The size of the cable supplying a property could be the limiting factor, three phase into domestic properties is common and may well be supplied by 4 x 6mm cable, which would make a single phase supply a bit iffy, the cable could be upgraded but it may be more trouble than it's worth depending on length/difficulty etc.

Edit. OP's probably still in the queue at the electric company office, they're hard work to deal with.
 
So what are the supply values/bands in France, that you get to choose from, for typical domestic installations??



[TABLE="width: 333"]
[TR]
[TD="width: 149"] Puissance souscrite.
(kVA)
[/TD]
[TD="width: 166"] Réglage Disjoncteur
(A).
[/TD]
[/TR]
[TR]
[TD="width: 149"] 3
[/TD]
[TD="width: 166"] 15
[/TD]
[/TR]
[TR]
[TD="width: 149"] 6
[/TD]
[TD="width: 166"] 30
[/TD]
[/TR]
[TR]
[TD="width: 149"] 9
[/TD]
[TD="width: 166"] 45
[/TD]
[/TR]
[TR]
[TD="width: 149"] 12
[/TD]
[TD="width: 166"] 60
[/TD]
[/TR]
[TR]
[TD="width: 149"] 15
[/TD]
[TD="width: 166"] 75
[/TD]
[/TR]
[TR]
[TD="width: 149"] 18
[/TD]
[TD="width: 166"] 90
[/TD]
[/TR]
[TR]
[TD="width: 149"] 24
[/TD]
[TD="width: 166"] 40
[/TD]
[/TR]
[TR]
[TD="width: 149"] 30
[/TD]
[TD="width: 166"] 50
[/TD]
[/TR]
[TR]
[TD="width: 149"] 36
[/TD]
[TD="width: 166"] 60

[/TD]
[/TR]
[/TABLE]


But this is not the whole story. Lower settings with 3 Phase unlikely - obviously :smile5: .
 
Often in this case the 4 wires are used as two pairs for monophase giving a total x-section of 12 mm2 - which would be counted as 10mm2 - at least temporarily :D
 
Three phase common in the countryside here in France - for agricultural use - pumps and so on. People often buy an old farmhouse and find they have 3 Phases - and usually the first thing they do is get it changed to mono - unless they are farmers and want to run motors and stuff ....... The disjoncteur de branchment is effectively an RCBO type "S" - which means it can be set to different sensibilities - but is sealed by the electricity supplier and can be set by an electrician contracted to do so by the supplier - but otherwise it is a criminal offence to break the seal -- I expect it is the same in Spain - from what I can make out here. A 12kVA three phase supply would probably be OK on three phase - 20 Amps per phase - provided the cookers and hotplates were appropriate and could be wired to more than one phase - which is often the case - (especially with induction). I always encourage customers with 3 phase to change to monophase unless there really is an electromechanical thing that is best with 3 phase ....... like a big irrigation pump !
 