Hi all I need some advice, I got a job coming where the customer requires to flood lights to light up his yard (so need to be quite bright) installed on a time switch positioned next to DB. question 1 = whats is a good 24 hour 7 day programmable time switch and good flood lights. question 2 = He wants 4 external twin sockets on same circuit to save on cable - I was gonna use 4mm 4 core one live for lighting feed in and out of time switch and one live for sockets and obviously neutral and cpc the run is about 55 metres any suggestions please
 
if using SWA, separate the neutrals and use the armour as cpc. then a fault on 1 circuit could be isolated without isolating both. recommend metal halides. they come in 70w, 150w, 250w. the 2 latter ones are the same gear, different lamp wattage ( those i buy are ), so you could fit 150's and if not bright enough swap the lamps for 250. must say thouh, i would prefer separate cables for the sockets and the lights.

edit: use a 3kwatt immersion heater timer (about £15). preferably the mechanical one.

​
 