Hi chaps, I was called out to a house to fix an outside light, once there I look at the light ask where the switch is?- there isnt one. - not since the rewire last year - which was done by niceic spark (who needs a swich when you've got a mcb!).

And when I was there they asked me for a price on a outside socket and more security lights.......

ZE is 0.11

I'm not sure what to do about this earth clamp? would you ignore it? tell homeowner to get norweb out to it? or just make a note on my cert?
 
From past experience the supplier will charge you £120 for turning the supply into pme
Or 200 for guy to come and sweat a joint on Or they may tell you turn it into TT

I have a mate that works for norweb and he supply’s me with braids witch clamp around the cable like a strap but are set with a tourk screw so when it gets tight it breaks off
Not being a bad spark but would leave the strap on the incomer and mark it as a code 4 departure

Hope this helps:cool:
Tapout
 
This is a common occurance in my area, Supply authority wont upgrade as they say they are not obliged to provide an earth. Our NIC Inspector does not accept this as a suitable earth and insists such installations are converted to TT (see snag 8 in "Snags and Solutions").

As for making a note on your cert bear in mind you shouldnt do any work on a property unless means of earthing and main bonding is up to scratch.

Regards
 

Reply to TNS Earth clamp? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi It’s a bad setup but I went for a call out in the night in a residential unit. There’s a rcd in its own enclosure feeding a 14 way board that...
Replies
3
Views
1K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K
Has anyone any knowledge on earth leakage clamp meters. As far as I can make out they are identical to a normal clamp meter only with greater...
Replies
7
Views
2K
P
The one good thing about this job is that after 15 years I'm still being amazed by what I find. So, welcome to the house with the wiring from...
Replies
2
Views
2K
I recently came across an installation, very rough in practically all areas, however one thing caught my eye. The TNS earthing arrangement was...
Replies
14
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock