Hi all, just looking for a bit of advice with regards to a new earth on a tns system. Should I take my new earth down to the clamp on the incoming cable or just to the met? I’m just wondering if I should be touching the clamp at all as it’s probably property of the dno? Ze is measured at 0.44 from the met.
 
Thanks for the info. So I am right in thinking that the clamp essentially belongs to the dno and I’m better off not touching it incase it snaps or shears?
If there's already a tail from the cable sheath to a block[MET] just connect into that, but if it's undersized by current standards I'd ask your local DNO to upgrade it.
 
Yeah it's not the right clamp, looks like a bonding clamp, which obviously shouldn't have ever been used. Pretty sure DNO clamps are usually angled on the inside so they don't cut into the or damage lead shefting and go BANG on the person tightening it up.
 
Well technically there's a Earthing conductor there, so just do your bit from the met and give them a call and just tell them the wrong clamp has been used and someone needs to come out a replace it, as it could potentially cause damage to the incoming supply.

Even if they do tell you to convert it to TT which they would prob tell you to do if the cable fell off the clamp, you would still have the issue of the wrong clamp being used.

We shouldn't be ever replacing clamps on the DNO or touching the clamps really. If you did and there was a problem I doubt wether our insurance would pay out either !!
 
Some DNO's use to fit these years ago, however now they have "lost" all data and dont have a record of providing TNS to the property.

I had this in south wales, called DNO - came out and quoted almost £200 to fit a new clamp.

Called NAPIT technical - Advised if readings are within limits its not our issue, make a note on the cert. Advise customer to liase with DNO.
 
I did read somewhere about some dno’s using them in the past. I’ll ring Stroma tomorrow and see what they say. I took a ze and it was fine (0.44).
Some DNO's use to fit these years ago, however now they have "lost" all data and dont have a record of providing TNS to the property.

I had this in south wales, called DNO - came out and quoted almost £200 to fit a new clamp.

Called NAPIT technical - Advised if readings are within limits its not our issue, make a note on the cert. Advise customer to liase with DNO.
 
Just to be clear. Never interfere with a BS951 clamp on the incoming cable. There is a real and distinct possibility of causing (especially older cables) a short and as mentioned a big bang. It is far too dangerous apart from the fact that you would be breaking the law. The risk factor is very high.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

TheCodboy

Arms
-
Joined
Location
Newcastle

Thread Information

Title
TNS earthing & clamp
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
TheCodboy,
Last reply from
The Ghost,
Replies
13
Views
6,867

Advert

Back
Top