Went to install a few extra sockets into dado trunking in an office, nice easy one for a saturday morning. Checked ring continuity at first socket to tap into ring, no continuity, went on to discover spurs off spurs big style, 6 sockets spurred off ring on one side of office, 7 spurred off ring on other side and two spurred off other side, all installed by an niceic approved contractor. This wasn't picked up on a recent periodic either.
 
Nothing is ever easy on a Saturday morning. You can guarantee you will run into problems that take hours rather than minutes :-(
 
calculate you load. probably quite low, computers etc. if load will allow, change breaker for a 20A. sorted.
 
The load is low but would need to seperate the circuits, as i was taught circuits should not be connected together.
 
might be a good idea to split into 2 radials. but a RFC on a 20A with spurs is compliant.
 
If there is a lot of potentially leaky equipment in that room you might want to consider high integrity earthing if it's radials just a thought
 