Hi All
thanks for feedback. Tested all circuits individually and results of IR are as follows

MAIN SWITCH
Circuit 1 Water Heater LE 1.2Mohms LN >299mohms
Circuit 2 lights LN-E 3.45Mohms
Circuit 3 shower LE >299Mohms LN >200Mohms (this circuit for some reason was installed without RCD protection)
RCD 1 63A 30mA
Curcuit 4 cooker LE 1.79Mohms LN 1.99Mohms NE 2.30Mohms
circuit 5 ring main LE 0.65Mohms LN 0.66MOhms NE 0.66Mohms
circuit 6-8 all heater Spurs again IR of between 2-6Mohms

Again whilst I was there I watched the main isolator (Wylex not an RCD) 'trip'???

as well as this tenant claims same is happening with the off peak main switch as soon as it kicks in at night.

Whenever I text a circuit for a 2nd time I get fairly different results

The problems start at about 4 and go on until approximately 9.30 in the morning.

Wondered whether there could be potentially some form of thermal damage where cables enter board above ceiling or something.

Has anyone ever seen a Main Isolator do this before??? It is the RCD tripping also however

thanks in advance


good update matey

best you change the isolator - I am surprised that it's tripping, And on the off peak board.

the 4am to 9.30am bit looks as if the off peak is on then - could you visit at 8.30 to see this first hand?
 
Sorry mate meant to say 4pm until morning. I will probably change both main isolators as a precaution. Have witnessed both main isolators 'trip' and the RCD when I was there Tuesday night about 10pm. So strange
 
Sorry mate meant to say 4pm until morning. I will probably change both main isolators as a precaution. Have witnessed both main isolators 'trip' and the RCD when I was there Tuesday night about 10pm. So strange

Now that is VERY odd. Are you sure that they are not 100mA RCD's?
 
Just got customer to email pictures for all you non believers lol image.jpeg
though it is a Wylex in an old MEM board however off peak is MEM main switchimage.jpegimage.jpeg
 
This is why I'm so confused. I've known this since I started in this game, spent an hour in the flat convinced they were saying it to keep me there until it was sorted and then it just clicked down. No bang or anything
 
It must be failing mechanically not trippy but i have never known that to happen , is tbe switch stiff to operate or very loose ad pete says could be a duff swich just odd that both switches have failed.
 
Then within 10 minutes off peak done the exact same. Rang my old man, who I done my apprentiship with and have worked for ever since, and he doesn't believe me either haha. But I swear it happened. I will try and get a video if I can when in next there, set one up for an hour lol
 
If you swap out these switches I hope you strip then down to see if theres any damage etc inside. Seen them melted holes in the side but never trip and 2 of them (maybe you need a priest:rolleyes4:)
 