Have you changed the unit? could be it's a duff Isolator
Haven't got a picture of the actual one but it is this
http://m.screwfix.com/p/wylex-100a-...d%20Lighting&gclid=CK3m4rH08soCFRSNGwoddRsPgw
i promise lol
Hi All
thanks for feedback. Tested all circuits individually and results of IR are as follows
MAIN SWITCH
Circuit 1 Water Heater LE 1.2Mohms LN >299mohms
Circuit 2 lights LN-E 3.45Mohms
Circuit 3 shower LE >299Mohms LN >200Mohms (this circuit for some reason was installed without RCD protection)
RCD 1 63A 30mA
Curcuit 4 cooker LE 1.79Mohms LN 1.99Mohms NE 2.30Mohms
circuit 5 ring main LE 0.65Mohms LN 0.66MOhms NE 0.66Mohms
circuit 6-8 all heater Spurs again IR of between 2-6Mohms
Again whilst I was there I watched the main isolator (Wylex not an RCD) 'trip'???
as well as this tenant claims same is happening with the off peak main switch as soon as it kicks in at night.
Whenever I text a circuit for a 2nd time I get fairly different results
The problems start at about 4 and go on until approximately 9.30 in the morning.
Wondered whether there could be potentially some form of thermal damage where cables enter board above ceiling or something.
Has anyone ever seen a Main Isolator do this before??? It is the RCD tripping also however
thanks in advance
Sorry mate meant to say 4pm until morning. I will probably change both main isolators as a precaution. Have witnessed both main isolators 'trip' and the RCD when I was there Tuesday night about 10pm. So strange
Its impossible for the main switch to trip....