Hi!

Need to pick some brains as I am truly stumped by this one

call out to a flat with nuisance tripping. On arrival tested circuits and all IR tests between LE were coming up relatively low, between 0.50-0.80 with the exception of ring main coming out as 0.01. There has recently been a leak from upstairs water tank so must be water somewhere, but at no outlet is there any sign of water (we checked lights, sockets, the lot) No sign of water in DB. Now the tenant told me not only was the RCD tripping but the main switch also. Now as far as I was aware these are isolator a only but low and behold whilst I was there I witnessed it trip, as well as the off peak board (was a late night call out).

For the sake of the tests, after removing the main fuse I also tested meter tails, showing up as 0.00 IR between LE but fuse won't blow and seems fine? Got my other fluke tester out as I was convinced my multimeter was going up the spout...same results.

Has anyone experienced anything like this? Either I'm not as good as I thought I was or the flat is haunted haha

any advice is massively appreciated!

thanks
 
When you were testing did you Isolate the Earths and Neutrals from the CU, if not did you test with the fuse out of final circuit but main switch on?

Don't forget the Earth is Strapped to Neutral at the DNO side if not a TT and you probably still have something in the circuit so you will get a very low L/E readout as it goes through the load, down the N to the E strap point hence your reading.

Remember the key points you were taught when doing IR tests or your reading won't mean jack.
 
Last edited by a moderator:
^ Agree...music,news,vaccinations...all work great going global... looking for a specific fault,requires specific testing. Individual results can then be studied,to build a better picture of what is happening.

Also, it is not clear whether you have identified the "main switch",as an RCD or isolator. If it is the latter,and you have witnessed it "tripping"...then there are stranger forces at work :devilish:
 
Hi All
thanks for feedback. Tested all circuits individually and results of IR are as follows

MAIN SWITCH
Circuit 1 Water Heater LE 1.2Mohms LN >299mohms
Circuit 2 lights LN-E 3.45Mohms
Circuit 3 shower LE >299Mohms LN >200Mohms (this circuit for some reason was installed without RCD protection)
RCD 1 63A 30mA
Curcuit 4 cooker LE 1.79Mohms LN 1.99Mohms NE 2.30Mohms
circuit 5 ring main LE 0.65Mohms LN 0.66MOhms NE 0.66Mohms
circuit 6-8 all heater Spurs again IR of between 2-6Mohms

Again whilst I was there I watched the main isolator (Wylex not an RCD) 'trip'???

as well as this tenant claims same is happening with the off peak main switch as soon as it kicks in at night.

Whenever I text a circuit for a 2nd time I get fairly different results

The problems start at about 4 and go on until approximately 9.30 in the morning.

Wondered whether there could be potentially some form of thermal damage where cables enter board above ceiling or something.

Has anyone ever seen a Main Isolator do this before??? It is the RCD tripping also however

thanks in advance
 
Circuit 3 thats because it's in a shower/bathroom I suspect
You watched the main switch not a RCD trip?????
 
Last edited:
Looks like its somthing to do with thd sockets could be a junction box under the floor full of water , is it posible to disconnect the socket circuit completly , adfor tns main switch triping is imposible unless the swich is warn and gravity to pulling it down which i have never seen or herd of
 
Hi All
thanks for feedback. Tested all circuits individually and results of IR are as follows

MAIN SWITCH
Circuit 1 Water Heater LE 1.2Mohms LN >299mohms
Circuit 2 lights LN-E 3.45Mohms
Circuit 3 shower LE >299Mohms LN >200Mohms (this circuit for some reason was installed without RCD protection)
RCD 1 63A 30mA
Curcuit 4 cooker LE 1.79Mohms LN 1.99Mohms NE 2.30Mohms
circuit 5 ring main LE 0.65Mohms LN 0.66MOhms NE 0.66Mohms
circuit 6-8 all heater Spurs again IR of between 2-6Mohms

Again whilst I was there I watched the main isolator (Wylex not an RCD) 'trip'???

as well as this tenant claims same is happening with the off peak main switch as soon as it kicks in at night.

Whenever I text a circuit for a 2nd time I get fairly different results

The problems start at about 4 and go on until approximately 9.30 in the morning.

Wondered whether there could be potentially some form of thermal damage where cables enter board above ceiling or something.

Has anyone ever seen a Main Isolator do this before??? It is the RCD tripping also however

thanks in advance


good update matey

best you change the isolator - I am surprised that it's tripping, And on the off peak board.

the 4am to 9.30am bit looks as if the off peak is on then - could you visit at 8.30 to see this first hand?
 
Sorry mate meant to say 4pm until morning. I will probably change both main isolators as a precaution. Have witnessed both main isolators 'trip' and the RCD when I was there Tuesday night about 10pm. So strange
 
Sorry mate meant to say 4pm until morning. I will probably change both main isolators as a precaution. Have witnessed both main isolators 'trip' and the RCD when I was there Tuesday night about 10pm. So strange

Now that is VERY odd. Are you sure that they are not 100mA RCD's?
 
Just got customer to email pictures for all you non believers lol image.jpeg
though it is a Wylex in an old MEM board however off peak is MEM main switchimage.jpegimage.jpeg
 
This is why I'm so confused. I've known this since I started in this game, spent an hour in the flat convinced they were saying it to keep me there until it was sorted and then it just clicked down. No bang or anything
 
It must be failing mechanically not trippy but i have never known that to happen , is tbe switch stiff to operate or very loose ad pete says could be a duff swich just odd that both switches have failed.
 
Then within 10 minutes off peak done the exact same. Rang my old man, who I done my apprentiship with and have worked for ever since, and he doesn't believe me either haha. But I swear it happened. I will try and get a video if I can when in next there, set one up for an hour lol
 
If you swap out these switches I hope you strip then down to see if theres any damage etc inside. Seen them melted holes in the side but never trip and 2 of them (maybe you need a priest:rolleyes4:)
 
I had a callout a couple of years back where the house holder swore 100% that the main switch on a 3036 board tripped several times over a 24hr period. Obviously on those boards there is only the one switch, so pretty much impossible to mistake it! The fella came across as not at all stupid and he had no reason to lie about it. I tried the switch several times and it didn't feel loose or sticky. I did say at the time they were just switches, with no internal mechanism that could cause it to trip.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)