Got a call out yesterday to look into a problem which has stumped me, and it seems many others before me.

Wylex 16th ed Box (installed 2005 by qualified registered spark who left good cert), 2 lighting, and door bell on main breaker together with a Hager bell transformer, shower sockets immersion, etc on 100a 30ma RCD.

When kitchen 18" fluorescent is switched "off", it regularly trips the RCD which obviously its not attached to.

The owner worries that on leaving the house and turning off the light the RCD will trip and the freezer will defrost during the day.

The lights switch is below a shower cubical, there is a socket on the opposite side of the door frame at light switch height, I've done an insulation test on the plaster work above the light switch say about 3 foot above and get 190meg and above the socket and get similar.

I started thinking about back EMF but can't figure out how anything from the fluorescent call leak across to the neutral of socket or shower or immersion circuit especially given that the RCD never goes when everything is on or if a bulb blows.

I measured trip times and the RCD seemed to react OK but don't have a ramp tester so I only suspect the RCD is OK

The only thing I can come up with is to put a bayonet fitting in the kitchen to try and move towards proving leakage out of the flurry (which others have replaced twice)

Any suggestions thoughts would be very welcome
 
Just an obvious one, but the neutral from lights is not on the rcd side, I know it should trip when switched on but worth checking

Chris
 
Thanks Chris/Murdoch, I think she'll agree they've been trying to fix it for some years now, the only reason I didn't do it yesterday was purely the fact that I can't think of how 30ma might be getting back to the RCD
 
My first step would be to wire a snubber across the switch contacts to eliminate any switching spikes.
 
Maybe the lighting circuit is wrapped around the heating pipes and that's what's providing a route back??
 
Something like a 0.1uF 240v inline with a 100ohm @ 5w ?

The capacitor will need to be rated for 500V since they are rated for peak voltage and not rms Volts
 
You're showing off now :devil2:

I can also drive no-handed with a blind fold, available for demonstration runs on a road near you !:43:
 
Had a similar problem with an old Grundig telly- I found out the telly discharged the charge in the tube through the ariel cable.

as others have said- change the light
 
  • Like
Reactions: 1 person
think my memory was back to front
seems to be switching on fluorescents with pfc caps
and switching off fluorescents without pfc caps
according to rcd handbook dec 2010 which i downloaded
and as already said arcing of contacts
so hopefully the snubber solves it
 
Mark/Dave Update, fitted snubber on Friday, had an email from the customer on Sunday saying all was well, fingers crossed! (I think they would normally have experienced a trip by then), haven't heard a thing since so....................

Carl
 
  • Like
Reactions: 2 people

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Tripping RCD - Unusual
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
leolec,
Last reply from
telectrix,
Replies
28
Views
279

Advert