£70-£100 nice Wago box for the main connection and a cable round each light, connect up and test. For the sake of a ton mate, just get it done properly.
Discuss Trying to install downlights into a room in the Lighting Forum area at ElectriciansForums.net
How much you reckon it'll be? We've already drilled the holes for the downlights ect. It's literally just the wiring.
£70-£100 nice Wago box for the main connection and a cable round each light, connect up and test. For the sake of a ton mate, just get it done properly.
Is that the case or is it for new lighting circuits?It's not 'just the wiring' the existing circuit needs to be checked to ensure that it is safe to make alterations to it.
The regulations have changed a lot and now require any new lights in domestic installations to have RCD protection so there may be additional work required.
[automerge]1599422644[/automerge]
What about RCD protection?
Assuming RCD protection is already in place.It's not 'just the wiring' the existing circuit needs to be checked to ensure that it is safe to make alterations to it.
The regulations have changed a lot and now require any new lights in domestic installations to have RCD protection so there may be additional work required.
[automerge]1599422644[/automerge]
What about RCD protection?
I guess its just like adding a new socket, just seems a bit harsh.Yes your part of the installation must comply to current Regulations.
I guess its just like adding a new socket, just seems a bit harsh.
However replacing an existing socket isn't.
What if the OP replaced the original fitting with a clik marshaling box, then its all plug and play?
Might be a struggle to get it through the downlight cut out though.