At the point you have shorted N and E, you have 2 paths back to the transformer, in parallel:
The neutral conductor, say approx 1 ohm, and
The earthing system, about 77 ohms.
To trip the 30mA RCD, gonna need >15mA straying to earth.
V = IR
V = 0.015 X 77
V between short and trans = 1.155V
I = V/R
I = 1.155 / 1
I in neutral conductor = 1.155A
So an absolute theoretical minimum of 1.170A flowing in the neutral at the short to trip the RCD (probably need a lot more in practice).
The current straying to earth might not come from that circuit, it might come from others on the same RCD. In which case the same calculation, but now the 2 paths would be:
Neutral conductor from N bar back to transformer, say about 0.1 ohm, and
N conductor of socket circuit from N bar to the short, then back to transformer via earthing system, about 78 ohms.
0.015 X 78 = 1.17
1.17 / 0.1 = 11.7A flowing in the N bar