They do, but I have only ever known them be made to order by specialist protection companies. I can't imagine them ever being used in anything other than a specialist installation, they aren't exactly cheap!

Yes indeed. I've had a quick search and such beasts can be ordered but surely putting these into a domestic situation for final circuits would mean that the tripping times required of 300mS @ 30mA and 40mS @ 150mA are not met.
 
OK, all credibility (as if I ever had any anyway) is about to be ruined!

Having checked the info, they are standard RCDs and not time delayed!! I was going on colleagues info (honest) and not physically checked the details myself. So all advice above is much appreciated and fully understood. It's all a learning process :sick:

Cheers
 
  • Like
Reactions: 2 people
Yes indeed. I've had a quick search and such beasts can be ordered but surely putting these into a domestic situation for final circuits would mean that the tripping times required of 300mS @ 30mA and 40mS @ 150mA are not met.

Yes exactly, they are no use for shock protection.
I think they see use as a backup fault protection when 10mA protection is used. But I could be wrong
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
TT Zs Readings and Tripping RCD?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
paulk11,
Last reply from
Deleted member 26818,
Replies
23
Views
5,426

Advert