Sounds like 28 days is when his sparky is next available.... If you had a sparks in to do some testing and he was happy, why did he not energize some of the circuits?
He did energize and the main contractor is not very happy about that, and I'm stuck in the middle trying to get my facts straight. Thanks everyone what a helpful community.
Reactions: DPG
My neighbour had a flood a few years ago, and although the water didn’t run through the CU, just the moisture in the air was enough to damage the breakers.
This didn’t stop the elderly father of another neighbour from turning on the power to give them lights…. Even though water was visibly running down pendant flexes.
First thing I did after the homeowner demanded his insurance company had me do the electrical repairs… was to install a temporary board for dehumidifiers.
I tested every length of cable, and only had to replace metal back boxes, new faceplates, new cabling for additional smoke detectors and a new CU at the end of the job.
Although he had a very good electrician… the joiner, plumber and labourer were idiots.
3 core between two way switches on staircase caught with a plasterboard screw. 3 separate water leaks which resulted in another new heat detector… and a gas leak!
Story over. There is no 28 day limit… but the installation needs tested before energising.
If in any doubt, a temp board can be fitted as soon as possible, leaving all of the installation not energised.
Even if the boiler wasn’t affected, damp could damage the internal board…. Or water got into a remote part of the heating system like a room thermostat. Best to leave it off too.
Can someone explain to me why the back box's need changing just because there is some effervescent contamination on them? seems to be padding the job IMO.
Reactions: nicebutdim
Possibly due to partial loss of sacrificial coating?
Had wondered about this myself as they're unlikely to suffer much corrosion if walls are dried out. Obviously if boxes presented evidence of corrosion to steel, for whatever reason, they should be replaced, but that's more likely to be a historic issue than one caused by moisture over the course of a month or so.
If the galvanised coating of the back box is damaged and the box has started to corrode then it is likely to continue regardless of how dry the wall is at any given moment.
It is sensible to replace everything which has been damaged by the flood.
I took it that Mike's point was related to undamaged boxes, but I guess corrosion could start at knockouts or where fixings have scratched away the coating.
Turning consumer unit on after water damage
ancienthistory,
nicebutdim,