Folks,

A bit baffled (not difficult) ... added a light switch in a rental this week (empty property so no social distancing issues) and checked the RCD before I signed off. It was a Wylex 80a 30mA and it failed all tests (inc. ramp) so I like-for-like replaced it. The new one also failed all tests (1/2, 1, 5 and ramp). Figuring I'd got a faulty one I replaced it again with the same results.

So ... surely not 2 new dodgy Wylex RCDs? Must be a problem within the installation? Tried testing the RCD on its own with no loads, same result. RCD stays on and the manual test trip works.

Megger MFT1552, 30mA range, Ze 0.29ohms, PFC 0.78kA.

Do I need to go to dead tests?
 
suspect a N-E fault on the installation. can do weird things to RCDS, does the RCD test button work?
 
Your test meter could be faulty.Maybe it doesn't like Wylex RCD's? Try it on a different make? You also need to be checking the RCD completely on it's own.ie take out the live and neutral terminals at the bottom of the RCD so it's completely stand alone and then try testing it again.If it now works then ,like others have said, it's probably a neutral fault.
 
Your test meter could be faulty.Maybe it doesn't like Wylex RCD's? Try it on a different make?

I did wonder. I've tested Wylex before and not had a problem. I also changed the batteries in case they were going bad. I'll check my RCDs here at home just to be sure though. Thanks
[automerge]1585507205[/automerge]
.... take out the live and neutral terminals at the bottom of the RCD so it's completely stand alone and then try testing it again.If it now works then ,like others have said, it's probably a neutral fault.

Aha, yes, makes sense to isolate the issue a bit more. I'll do that too.
 
Last edited:
OK, thought I'd update you all on this one.

Yes indeed, there was a fault between N and E. I isolated the RCD which then tested fine. I then disconnected the earth(s) for the lighting circuit - the first circuit I checked - and the RCD then tested fine. I reconnected each of the 4 (!) lighting radials one at a time and found the fault on the downstairs lights.

I'm currently looking for where exactly the fault is but it's certainly not in a light or a switch as I checked those already. Screw through a cable likely ...

Thanks for the help here guys.
 
if it was a neutral earth fault how come it wasn't tripping the rcd straight away. ive had a issiue with rcd that don't reset because of neutral earth fault

No idea I'm afraid ... not been able to get back there yet to look / check. Maybe I disturbed something somewhere. It is now a new RCD so perhaps the original was indeed faulty
 
Depends on whether the neutral/earth fault causes an imbalance. Just because you have a neutral/earth fault it should not be assumed the circuit will follow the earth path, circuit impedance may dictate the circuit carries on down the neutral path hence no imbalance.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cornwall

Thread Information

Title
Two new Wylex RCDs both failed tests
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
steamboatwilly,
Last reply from
Lucien Nunes,
Replies
15
Views
3,328

Advert

Back
Top