It is completely relevant that it tests ok. What are you on about?
I explained in the text you quoted.
It is completely relevant that it tests ok. What are you on about?
All the above are C3 recommendations and do not warrant an ‘Unsatisfactory’ report.
its down to the inspector on testing weather putting down a N/V or F1
he is the one will have the conscience .but the next person who test after him will say what a F**k idiot .
Works for me.'Oh bugger I've forgotten the earth rod, ah I know lets bury that old bike frame and connect to that instead !'![]()
Do we all accept that an EICR is a report on the condition of an installation at the time of the Inspection and Testing?
Can anyone explain why either the water pipe or gas pipe would be used as an electrode, and then bonded?
Is 63Ohms a good or bad reading for an earth electrode?
Does it indicate any instability?
Finally, who believes that the outcome of the Further Investigation would lead to a code C1 or C2?
It is the point though.
FI should be used for instances where it is suspected either a code C1 or C2 is present, but cannot be discovered for whatever reason.
This is copied from the notes on the 18th edition EICR model form:
“Where an observation requires further investigation (FI) because the inspection has revealed an apparent deficiency which could not, owing to the extent or limitations of the inspection, be fully identified and further investigation may reveal a code C1 or C2 item, this should be recorded within Section K, given the code FI and marked as unsatisfactory in Section E.”

Zs's were around 8 ohms.I know it's hindsight now, but you can always confirm bonding conductors with them disconnected using long lead test if unsure.
I think it just down to your judgement. As Ze is very acceptable, I would say either FI or LIM are perfectly reasonable.
Out of interest what sort of Zs's were you getting with bonds reconnected?