why do we have to do the calcs to 230v when the supply never is 230v

measured voltage at source is 248 volts at the site i am on at the moment ,

can somebody shed some logic on the idea before i start engineering an 18 volt drop into my cable sizes

( a joke of course but why not ? ) :ihih:

It may be 248v today, 235v tomorrow, 224v next week on that site.
Which voltage are YOU going to use?
 
Another consideration is that high voltage drop in a circuit implies high circuit impedance. So variations in load will produce large changes in voltage. I suspect that this is one reason for the lower permitted VD where lighting is present, as changes in voltage, and therefore light output, are particularly noticeable with traditional lighting types. Of course, with LEDs supplied by regulated drivers, this isn't an issue.
 
its done live.

Well I cant comment on all trannys and my HV experience is limited but ime pretty sure ours has a sign on the side saying it has to be done dead?

Either way I stay well clear of the damned thing LOL
 
do the transformers have to be de energised to change taps or do they bang it live ?

its done live.

Switched live they will go bang, don’t even think about it.

On load tap changers are normally at the 33/11KV transformers.

Off load
TapChanger-1.jpg


On load
Tap-Change-4_zpsc9e20d66.gif
 
Switched live they will go bang, don’t even think about it.

On load tap changers are normally at the 33/11KV transformers.

nice animated diagram.

recently read a HSE report that was linked on the IET forum that reported on the death of a sub station worker that was killed changing the taps manually - the mechanism connected to the operating handle failed , jammed between 2 of the contact points , chamber overheated , explosion with hot oil ensued with no warning - terrible way to go , DNO's subsequently changed their proceedures etc.
your 2nd pic is exactly the same as the technical video shown by the HSE
 
Last edited by a moderator:
nice animated diagram.

recently read a HSE report that was linked on the IET forum that reported on the death of a sub station worker that was killed changing the taps manually - the mechanism connected to the operating handle failed , jammed between 2 of the contact points , chamber overheated , explosion with hot oil ensued with no warning - terrible way to go , DNO's subsequently changed their proceedures etc.
your 2nd pic is exactly the same as the technical video shown by the HSE

That was terrible and I feel so sorry for the guy’s family.

There was a known fault on the tap changer and he operated it live.

Operating a tap changer isn’t a nice experience, the transformer sounds like its being violently sick.
It would be very rare you did it using manual control, they are normally under the control of a automatic voltage regulator.
If you watch the animation there are times where there are shorted windings which is where the two reactors (inductors) come in to play. They limit the current in the shorted windings.
 
Im pretty sure that the minimum is 216V for tolerances allowable if l remember correctly. Please put me right if im talking piggie-excrement. I think its nominal voltage 230 -6%=13.8V which is 216.2V to +10%=23V which is 253V...
I ask this question to the DNO just the other day and that's the answer they gave me too, The customer had a load of them GU10 compact florescent lamps that were only lasting a few months (the voltage was around 149 volts at the lamps and 151 at the incomer) The lamp supplier said that due to the higher voltage the lamps could be over heating ,mind you they are discontinuing these lamps so suggested fitting LED lamps instead.
 
Nominal voltage 230v permitted tolerance +10% / -6% 216.2 v - 253.0 v (bs7671, appendix 2, section 14).

Volt drop- 3% for lighting circuits, 5% for other circuits.

Probably repeated what others have said earlier..so apologise if so.
 