why do we have to do the calcs to 230v when the supply never is 230v
measured voltage at source is 248 volts at the site i am on at the moment ,
can somebody shed some logic on the idea before i start engineering an 18 volt drop into my cable sizes
( a joke of course but why not ? ) :ihih:
its done live.
its done live.
do the transformers have to be de energised to change taps or do they bang it live ?
its done live.
Switched live they will go bang, don’t even think about it.
On load tap changers are normally at the 33/11KV transformers.
nice animated diagram.
recently read a HSE report that was linked on the IET forum that reported on the death of a sub station worker that was killed changing the taps manually - the mechanism connected to the operating handle failed , jammed between 2 of the contact points , chamber overheated , explosion with hot oil ensued with no warning - terrible way to go , DNO's subsequently changed their proceedures etc.
your 2nd pic is exactly the same as the technical video shown by the HSE
Im pretty sure that the minimum is 216V for tolerances allowable if l remember correctly. Please put me right if im talking piggie-excrement. I think its nominal voltage 230 -6%=13.8V which is 216.2V to +10%=23V which is 253V...
I ask this question to the DNO just the other day and that's the answer they gave me too, The customer had a load of them GU10 compact florescent lamps that were only lasting a few months (the voltage was around 149 volts at the lamps and 151 at the incomer) The lamp supplier said that due to the higher voltage the lamps could be over heating ,mind you they are discontinuing these lamps so suggested fitting LED lamps instead.Im pretty sure that the minimum is 216V for tolerances allowable if l remember correctly. Please put me right if im talking piggie-excrement. I think its nominal voltage 230 -6%=13.8V which is 216.2V to +10%=23V which is 253V...
yes used 2 different tester to check149/151 volts are you sure?
yes used 2 different tester to check