Hi,

Im a fairly new sparky,
So just wanted to get a little idea as im not 100% sure,
Im adding 12m of 1.5mm cable in trunking into a conservatory from a fcu of the ring main the volt drop for this part would be 4.5v so i may need to up the cable size. But what i need to know or confirm is what would i take the ring main volt drop as, as if it was a short run it would be no problem. ? Any suggestions would be helpful and of coarse i will follow it up with my own research when i get a sort of idea.
 
Last edited by a moderator:
[COLOR=rgba(0, 0, 0, 0.701961)]Hi,[/COLOR][COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Im a fairly new sparky,[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]So just wanted to get a little idea as im not 100% sure,[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Im adding 12m of 1.5mm cable in trunking into a conservatory from a fcu of the ring main the volt drop for this part would be 4.5v so i may need to up the cable size. But what i need to know or confirm is what would i take the ring main volt drop as, as if it was a short run it would be no problem. ? Any suggestions would be helpful and of coarse i will follow it up with my own research when i get a sort of idea.[/COLOR]

??????
 
Hi,

Im a fairly new sparky,
So just wanted to get a little idea as im not 100% sure,
Im adding 12m of 1.5mm cable in trunking into a conservatory from a fcu of the ring main the volt drop for this part would be 4.5v so i may need to up the cable size. But what i need to know or confirm is what would i take the ring main volt drop as, as if it was a short run it would be no problem. ? Any suggestions would be helpful and of coarse i will follow it up with my own research when i get a sort of idea.
 
Hi and welcome.

Firstly 4.5V sounds very high for 12m of 1.5mm. You've maybe made an error there.

You can calculate the length of the ring final by measuring r1 or r2 (end to end of live or the cpc). You can then calculate the cable length by finding the ohms per metre for the cable size that's been installed.
 
Last edited:
Can you show your calculation method so we can correct it, or use copper as a conductor because 4.5v for 12m of 1.5 is definately wrong, if you think about it your lighting in your house would have a max' length of about 16m before it failed its VD if in 1.5...!
 
Last edited by a moderator:
29x12x13 %1000 =4.524v
mV/a/m-Meter-Amp
In trunking
 
Last edited by a moderator:
I understand the high VD now, just from a design point of view can I query how the conservatory is been heated, will it be likely to have a heater plugged in?

ps Over Current Protective Device OCPD
 
So the 13 amp fuse basically would be the ocpd , never heard of it being said as ocpd
No heater no....?
 
Last edited by a moderator:
You have to add the VD you calculated for the radial spur to the VD calculated for the ringmain, if this does not comply for the ring then redesign your circuit or increase the cable.

Volts drop is always calculated from source to end point but where you fuse down mid point you calculate each section and add together.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Volt drop
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
Maxstone89,
Last reply from
Maxstone89,
Replies
23
Views
2,944

Advert

Back
Top