Hi
I recently had a PV system we installed switched off after the Electrical Contractor got a shock off the Neutral. He was wiring lighting but after a processes of elimination found the fault was on our PV circuit.
We did dead tests on the circuit
Insulation resistance (1000v)
Continuity
Polarity
But no faults came up. He would not let us re connect it until the fault was found. Now the question:
He would let us connect the live but not the neutral (in case it livens up all the neutrals and earths in the school), so live and earth was connected to their DB). We disconnected the PV system so we just had a 20m 3 core flex from plant room to roof. When the live was connected to he live DB we would get 104v across neutral (not connected to DB and earth (connected to the DB)
When the micro-inverters were connected we would get 240v across earth to neutral.
When we finally connected the neutral to the DB the voltage between earth and neutral dropped to 1v.
Anyone shed any light on this? Happy to give more info if it's not clear but it's a long post already.
Thanks people
I very much doubt there was a fault on your installation which was causing the electrician working on lighting circuits to get a shock from a neutral.
How did he decide the fault was on the PV installation?
Telling you to connect the live and cpc of your circuit and not the neutral is dangerous and absolutely pointless as an energised circuit with the neutral disconnected will give you a voltage on the neutral if there is something on the circuit switched on, as you found out!
Yep,there is a host of details required,here...not least of all,what instrument was used to measure the voltage.
My guess would be there is a small leakage current flowing in the earth line, because when he took the first measurement this system was NOT grounded properly, so this current had no where to go. So it took the path thru the main bond and up the neutral line.Once the system was grounded properly, this small leakage current will bleed off thru the ground.
Cheers for the comments so far. Happy to give more detail:
Earthing: PME
Testers: Fluke Multi-function and Ethos Multi-meter
How he decided it was a fault on my circuit:He spent awhile disconnecting each lighting circuit, then switched off each MCB, my circuit was one of the last.
When you say the system was not grounded properly, do you mean my circuit or all circuits. My first fault finding was to go over all my connections and visually inspect the cables and all was perfect. If you mean the whole installation, he did the same on his DB.
But no faults came up. He would not let us re connect it (the neutral) until the fault was found.
"he" is not an electrical contractor then ................. and why didn't he just switch off the PV system?
Focus people. I'm asking a specific electrical question not asking for judgment. If there are gaps in the explainstion then show your experience and ask specific questions.
Murdoch- re read the OP. He switched off the circuit
Suffolkspark: Re read the last line of the OP. Happy to give more info. What would you like to know?
I'm thinking perhaps a wiring polarity fault in that circuit or problem with floating N?
Related thought - TNCS system has N and E solidly connected at the cutout. Verify. Then I'd be using wander lead to see what's actually connected to what, as large N-E voltages shouldn't happen.
Wilko, yes we went through all that. The Electrical contractor thought it might be to do with the LPS.
But floating Neutral seems to be the key word here. I found a great article explaining it
IET Forums - Floating neutral? - https://www.----------/forums/forum/messageview.cfm?catid=205&threadid=103200
I'm thinking
1) The initial Neutral fault on the system wasn't from our circuit after all
2) As Streamer mentions, our testing procedure was flawed by dis-connecting the neutral (and creating a floating neutral). I didn't think that, by dis-connecting the neutral of a cable (even when not connected to a load) would mean I would get a voltage reading from neutral to earth when the live of that cable is connected.
I think I've been nicely schooled here, but still open to other comments/opinions on this.
We can't do an insulation resistance test on the micro-inverters so the cable was dis-connected and terminated in a connector block.