Sorry Andy78 you lost me ccc refers to correct carrying capacity?
Load is 27amps
That's why I wanted to go for 6mm.
The voltage drop formula was to ensure it would be compliant.
Is this not the correct way?
Load is 27amps
No not really. This thread has been concerned only with VD and you wanting to work out the minimum size cable for VD.
If you want to make sure your selected cable for CCC complies with VD, then it's a different process and a different formula.
Standard cable design process has you sizing the cable appropriately for CCC requirements taking into account derating factors, then you check for compliance with volt drop.
And you will need to know the actual volts dropped over your distribution cable so you can work out the remainder of VD left for your final circuits from your outbuilding CU.
I just picked a random machine from screw fix.
http://m.NoLinkingToThis/p/record-power-pt107-265mm-planer-thicknesser-240v/48940
I've created a essay/document to test my knowledge and that I could refer back to.
I was designing the circuit. This thread is in relation to powering a shed.
I know this is veering slightly from the plan.
Load of 27A on a buried SWA cable run for 25m from the origin of the installation.
Load is 27A so a 32A breaker required, cable must be able to take 32A.
Current carrying capacity of SWA method D no other rating factors in table 4D4A:
2.5mm² has 29A not enough for 32A breaker.
4.0mm² has 37A OK so the minimum cable size so far is 4.0mm².
So for a 4.0mm² cable the volt drop is 11 mV/A/m.
Using the values we now have in VD = (mV/A/m x L x A)/1000
Volt drop = (11 mV/A/m * 25 m * 27 A)/1000
Volt drop = 7.425 V
maximum volt drop for power is 11.5 V (5% of 230 V) so this is OK for power.
maximum volt drop for lighting is 6.9 V (3% of 230V) so this is not OK for lighting
OK so move up to 6.0 mm² cable with a volt drop of 7.3 mV/A/m as it is a bigger cable the current carrying capacity is going to be OK.
Volt drop = (7.3 mV/A/m * 25 m * 27 A)/1000
Volt drop = 4.93 V
maximum volt drop for lighting is 6.9 V (3% of 230V) so this is OK for lighting.
Therefore for this run of cable, assuming the cable comes from the origin and does not have a significant circuit length to supply the sockets and lights and machinery in the shed, and for this installation method carrying a design curent of 27A, the minimum size cable that can be used to supply lighting is 6 mm².
Thanks Richard I was struggling with the calculation it self.
I wasn't happy with myself for getting the answer but not understanding the calculation.
Thank you for clearing this up for me. I think I owe you a few by now.
Thanks again Richard :)
Reply to Voltage drop workout in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
can anyone tell me if this is a correct way of thinking i have 6 Cleaners outlets off a !6a rcd, total run length is 55m 6mm feed to first point...
When calculating voltage drop and using the formula mV/A/m x Design Current x length / 1000 = v Do I use the design current value after rating...
Select (Scottish) Certification Scheme Question on volt drop from 2391
Hi all, I have worked out the volt drop on other questions using the formula mVxAxM. had no issues, but this question below has just fried whats...
6K