Also, watch for the surge current on start up of that machinery. Put a big lathe or something in there and the start up current could well be 3 times the nominal rated current, so you could end up with a 15% VD on start up.
I remember one fault report with an inverter on one of the forums that turned out to be caused by the inverter tripping out due to the massive voltage swing when a big bit of machinery started up in the shed it was connected in to.
Also when doing these calcs, if you could double check them to be sure to meet the 1% VD limit for a 16A solar PV supply that'd be much appreciated. Nowt worse* than having to dig the driveway up to install solar on the garage because the existing supply to the garage doesn't quite cut it for our purposes.
*ok there are actually quite a few things worse than that.
Reply to Voltage drop workout in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
can anyone tell me if this is a correct way of thinking i have 6 Cleaners outlets off a !6a rcd, total run length is 55m 6mm feed to first point...
When calculating voltage drop and using the formula mV/A/m x Design Current x length / 1000 = v Do I use the design current value after rating...
Select (Scottish) Certification Scheme Question on volt drop from 2391
Hi all, I have worked out the volt drop on other questions using the formula mVxAxM. had no issues, but this question below has just fried whats...