I use my trusty multi meter which is a Metrel.
Otherwise I use my Megger MFT for everything.
 
t140

The t140 is total sh*t. Useless to test to earth as you need to test to neutral first otherwise it'll take out a 30mA rcd. Not helpful when you don't have a neutral, ie light switch. It also does lots of odd things like flashing the digital screen or blips and it makes a awful noise when sensing voltage. Just buy a t5-600, now that I like.
 
Hi all,

new to the whole "voltage tester" thing im not sure what the good quality yet inexpensive brands are.
Have you had, or known of anyone to have experience with CEM? DI-logic and martindale?

Im looking for a voltage tester that isnt going to draw much more than 5mA and thus not tripping the RCD off..?

many thanks

I would also recommend looking at a Martindale. More specifically the VI13700/2. Really simple to use with four test lamps lit up by the voltage measured (50V, 100V, 200V, 500V).
The tester does not require batteries and is also guaranteed to not draw current above 5mA and trip RCD's. The tester is fused with retractable probes and is fully GS38 compliant.
And on another note, they NEVER go faulty.

It does't have features of some other voltage testers like measuring continuty, buzzer, LCD display, phase rotation indicator but for voltage detection and proving dead it is the ideal tool in my opinion.

Lasse
Test-Meter
 

OFFICIAL SPONSORS