ChrisElectrical88

-
Mentor
Arms
Afternoon Gents,

Came across a nice scenario today. Water pipe comes from the street, into the kitchen through a concrete floor. 100mm of copper behind a kickboard where it comes through the concrete 300ish mm of Plastic Pipe, 100mm of copper then stop tap. 90 percent of the installation is copper. IR from disconnected MET to first 100mm of pipe is 967 Ohms, After the plastic pipe its 28K Ohms, obviously over the 23K Ohms recommended.
First time i have come across an Insulated Section (Thats not the big blue water main.)

Would you bond and why?
 
Basically there is a plastic piece of pipe 300mm ish long 100mm away from the water pipes point of entry, under a kickboard so inaccessible.
Reading after the plastic pipe to the met is more than the 23 K Ohms revommended.

Im just making sure i havent missed a point in 411.3.1.2 which discribes this exact scenario.

Upstairs lights, alarm and dporbell have no additional protection
 
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.
 
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.

Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding

So it actually states in the reg it concerns metal services entering the building
 
I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

ChrisElectrical88

Mentor
Arms
-
Joined
Location
Wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Water bond, Insulated Section.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
ChrisElectrical88,
Last reply from
ChrisElectrical88,
Replies
21
Views
2,923

Advert

Back
Top