Search the forum,
Discuss What a normal r1 = r2 result should be on a light circuit in the UK Electrical Forum area at ElectriciansForums.net
S
scintillasam
Hi,
I just done a job today and got some reading of 7ohms, on continuity of a light circuit (B6 CB) this is the highest I have yet seen
is this still ok? Or is this a problem?
Cheers
either you've got an extremely long circuit, or bad connections. yes. 7Ω is a priblem
about 0.7Ω-- 1/10 of what you say you are getting.
if so i nominate him for one of these:
and when are some guys going to learn the difference between r1 an R1? it's like meerkat and market. different words, different meanings. ssssimplesss
Was there a switch in circuit? Poor/dirty contacts can cause high readings. Operating the switch a few times will often produce a better results.
Hi,
Cheers
theres no fixed value for R1 R2....just a suitably low value....but 7 ohms?...
come on what do you think...
for a start it wont meet a Zs for a 6A MCB to BSEN60898...will it...
Move to another point on the lighting circuit and retest then compare the readings.
Loose connection IMHO - are the CPC's twisted together or connected "properly"?
Thats why I put theoretically. Done an ecir last year where the tenant had a very damp wall and the zs was 316 ohms! My boss told me to leave it as that was within regs. Don't agree with it myself
no...its p!ss poor....
we have the means to get it down to a decent level....so why take the half arsed approach to it all?...
beats me....
Thats why the EICR needs a C4 - requires investigation.
If the circuit is short then the reading should be lower, I have had higher readings than i would normally expect & found the switch to be the problem as has been mentioned. Best to work your way along its length if that is possible.
A. 7 ohms is rubbish but within regs for a B6. ( Rule of thumb is advisory not a reg before anyone says its 6.18) .
B. Zs of 300 odd ohms? Depends on the earthing system, not sure what a damp wall has to do with it, its not IR.
C. I change maybe 5 faulty RCDs a month, anyone who relies entirely on a single RCD for protection is asking for trouble.
Reply to What a normal r1 = r2 result should be on a light circuit in the UK Electrical Forum area at ElectriciansForums.net
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...