R

Rauer

Hi been asked to do an emergency lighting cert for a company I do a fair amount of electrical work for , is there any particular course or registration that I need?
 
No you do a monthly test which is switch off and prove there all working and a yearly test were you do the 3 hour test you can down load the Certs
 
  • Like
Reactions: 1 person
BS 5266 says where national regulations do not apply the following checks shall be completed:

Daily:
Visual confirmation of LED indicators, central battery cubicles, self-contained units etc.
Monthly:
Duration testing (Partial Duration)
Check condition of fittings, present? Clean? Functioning correctly?
Annually:
Duration testing (Full Duration)

The reason for partial duration on the monthly test is to limit the risk posed by draining the batteries do. If there was a true emergency just after you had just completed a full duration test the emergency lights would not have had sufficient time to fully recharge.

BS5266 says a log book shall be kept on the premises in the care of a responsible person appointed by the occupier/owner and shall be readily available for examination by any duly authorized person.

The log book shall be used to record at least the following information:-

  1. Date of commissioning including certificates
  2. PIR dates
  3. Dates & brief service details, inspection or test
  4. Dates & brief details of any remedial works
  5. Dates & brief details of any alterations to the system
  6. If any auto test devices exist, the main characteristics and the mode of operation shall be described.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
What do I need for a emergency lighting cert
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Rauer,
Last reply from
1shortcircuit,
Replies
4
Views
1,567

Advert