Hi been asked to do an emergency lighting cert for a company I do a fair amount of electrical work for , is there any particular course or registration that I need?
No you do a monthly test which is switch off and prove there all working and a yearly test were you do the 3 hour test you can down load the Certs
Reactions: 1 person
BS 5266 says where national regulations do not apply the following checks shall be completed:
Daily:
Visual confirmation of LED indicators, central battery cubicles, self-contained units etc.
Monthly:
Duration testing (Partial Duration)
Check condition of fittings, present? Clean? Functioning correctly?
Annually:
Duration testing (Full Duration)
The reason for partial duration on the monthly test is to limit the risk posed by draining the batteries do. If there was a true emergency just after you had just completed a full duration test the emergency lights would not have had sufficient time to fully recharge.
BS5266 says a log book shall be kept on the premises in the care of a responsible person appointed by the occupier/owner and shall be readily available for examination by any duly authorized person.
The log book shall be used to record at least the following information:-
  1. Date of commissioning including certificates
  2. PIR dates
  3. Dates & brief service details, inspection or test
  4. Dates & brief details of any remedial works
  5. Dates & brief details of any alterations to the system
  6. If any auto test devices exist, the main characteristics and the mode of operation shall be described.
What do I need for a emergency lighting cert
Rauer,
1shortcircuit,
About us
  • Electricians Forums™ is a Recognised (unregistered) Trademark in the UK owned by Untold Media® which IS a Registered Trademark in the UK. We use the Trademark under licence and pay an annual fee of 250,000 GBP for it. Anybody found using the mark is liable to pay for the licence of it, and the legal costs, and court costs. We are aware of a Welsh company using the mark without permission and have activated Defensive Measure (legal route), and Offensive Measures (many that will damage their forum long-term) to take the website down via a number of routes, and to de-rank it in Google who are on our side in this case. CloudFlare is next, then XenForo who host it. Then Nominet. Then we should be able to take over the domain and shut the forum down.