I believe the product standard used to be a lot higher. Off load I thought it was about 270V.230v
Agreed, 'Off Load' the Output Voltage could be higher than the 'Nominal 230v' expected.Off load I thought it was about 270V.
If someone has an older model it could be suppling more than 230V.
With a transformer.What is the maximum output voltage permitted on a 230 / 115 Volt Shaver socket?
There it is in B&W cant argue with that ....... thanks mainline, hope that answers the OP's query!Neither the rated supply voltage nor rated output voltage of a shaver supply may exceed 250 V AC The no-load output voltage is not to exceed 275 V and the difference between the no-load output voltage and the output voltage under load shall not exceed 20 % of the load output voltage.