Trev is always welcome and it is good to see you back matey I and a lot of others have missed you now can you put these silly sods straight about testing rcd's in the way only you can:rofl:
Thanks for that Glenn. I think I just did though but just in case....
In an IV you've done your tests in the correct order so you know the circuit is in an acceptable condition. You're then going to carry out an RCD test. IE, you're testing the device. So can anyone please explain why you're considering carrying out your test in an incorrect manner.
On an EICR, it doesn't matter which order you carry out your tests as the circuit is already in service. However, at some point you're required to test the device. Not the bloody circuit because you've most likely already done that. So the same applies, why the almighty bloody hell are you proposing to carry out the test in an incorrect manner?
All this is Janet and John stuff lads, it's all there in the books that we're supposed to have a thorough working knowledge of.




See Glenn, never said **** or upset anyone. Told you I could do it :)
 
I was just saying I know that other test methods are not precluded , not that the op is correct lol.

Edit: Forgot to quote Trevs post lol.
 
Last edited by a moderator:
However, if there is no load you can test at the RCD without disconnecting the circuit.

No, because the circuit conductors are still connected and can skew the test result.

You are testing the RCD device, not the RCD + outgoing conductors or anything else.
 
Yes it does, the bit where it said "the test should be conducted at........."
Nice to see somethings never change on here guys.

Who are you? :wink:
 
NICEIC ALLOW rcd test to be done at the socket.

on my yearly checkup, id put in a new socket radial circuit, he asked me some questions and then to show him how i carried out all my testing, hes said nothing when i showed him an rcd test via the socket.
 
NICEIC ALLOW rcd test to be done at the socket.

on my yearly checkup, id put in a new socket radial circuit, he asked me some questions and then to show him how i carried out all my testing, hes said nothing when i showed him an rcd test via the socket.

so what? It's written in black and white how the test should be conducted for the reasons mentioned in various other posts on this thread.
 
Last edited by a moderator:
Kurtis, the NIC make their own rules up. Maybe the inspector was clueless, there's a few of them about. Check out the post which quoted GN3 mate.
 
Its states the load should be disconnected from the test, basically disconnect anything from sockets ect,
As thats the load, now theres nothing using current (load) it doesn't state it has to be done at the rcd, it actually states between the line conductor of the protected circuit and the associates cpc. Which can mean it can be done on a socket
9a3e82a0dbf05d56a21af91bb1ddff01.jpg
 
Mate, several pretty well respected people on here have told you the correct way to carry out this test. GN3 tells you how to do the test. The MIs will tell you how to do the test.
Why are you clinging to your incorrect method?
 