Okay, I know you have to use TT on a temporary building supply but cannot understand why? If the supplier is able to supply a TNCS why is this not preferable to a TT?
Section 704. 704.411.3.1
A PME earthing facility shall not be used for the means of earthing for an installation falling within the scope of this section unless all extraneous-conductive parts are reliably connected to the main earthing terminal in accordance with Regulation 411.3.1.2.
NOTE If the PME earthing facility is considered for use, see also BS7375.