plums1_2001

Hello,

I have purchased a new extractor fan and need some advice.

I have 4 cables
L - Brown
N - Blue
E - Green/Yellow
Live Switch? - Yellow

My new fan only has connections for 3 cables
L
N
E

I understand that the new fan probably hasn't got a timer function (isn't a problem) and will turn on and off with the wall switch.

My question is: if I connect the live switch to the live connection what do I do with the redundant permanent live wire?

Thanks in advance.
 
If a timer fan was required before in the room then the building regulations state that you should not make compliance any worse than it was before, so having a non timer fan may breach this requirement, however the 15 minute overrun requirement only applies to rooms without openable windows.

Regarding the permanent live connection this should be terminated in an insulated connection within the fan body.
You could use a terminal block or a push fit or lever action connector, so long as the cable is fully enclosed and will not pull free, just taping it over is not suitable.
 
Hello,

I have purchased a new extractor fan and need some advice.

I have 4 cables
L - Brown
N - Blue
E - Green/Yellow
Live Switch? - Yellow


My new fan only has connections for 3 cables
L
N
E

I understand that the new fan probably hasn't got a timer function (isn't a problem) and will turn on and off with the wall switch.

My question is: if I connect the live switch to the live connection what do I do with the redundant permanent live wire?

Thanks in advance.

I'm not sure you'll have these colours unless some conductors are sleeved
 
I'm not sure you'll have these colours unless some conductors are sleeved

Hi, to be honest the live may have been red it was hard to see at the time as it was a bit dark in the loft. Would this make more sense?
 
It was only an observation really. The colours aren't important (generally) so long as you identify and 'flag' them. RB's posts are helpful, informative and polite
 
Hello again,

Could I use a closed end wire crimp connector?

Thanks
You could, but remember that if you needed to change the fan to a timer model at a later date that you would then need to cut the cable to gain access to the conductor and it may then be too short to reach. If you have plenty of length then no problem.
 
as richard said. and the brown is most likely red. also, you need to be sure which is perm L and which is switched ( between red and yellow. this should be clear if you look in the light fitting and the switch.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Wiring advice - bathroom extractor fan
Prefix
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
plums1_2001,
Last reply from
Octopus,
Replies
10
Views
3,553

Advert

Back
Top