Hi, I hope you are all well. I want to ask if there are any considerations to wiring if installed in a cavity wall with soundproofing? Also, do sockets, etc. need to be incased with putty or sealed with sealant?
 
Have you any information on the soundproofing material?

Certainly cable needs to be de-rated to allow for thermal insulation and the most obvious thing to do from an electrical point of view is to assume the acoustic material is the same as it is unlikely to be better as thermal insulation!

Not sure about your point on the sockets. Are you concerned with fire-retardant stuff or is this about maintaining the acoustic properties of the wall?
 
Have you any information on the soundproofing material?

Certainly cable needs to be de-rated to allow for thermal insulation and the most obvious thing to do from an electrical point of view is to assume the acoustic material is the same as it is unlikely to be better as thermal insulation!

Not sure about your point on the sockets. Are you concerned with fire-retardant stuff or is this about maintaining the acoustic properties of the wall?
No info
Have you any information on the soundproofing material?

Certainly cable needs to be de-rated to allow for thermal insulation and the most obvious thing to do from an electrical point of view is to assume the acoustic material is the same as it is unlikely to be better as thermal insulation!

Not sure about your point on the sockets. Are you concerned with fire-retardant stuff or is this about maintaining the acoustic properties of the wall?
No info on the material yet. Yes, I was wondering about them being weak spots in the sound insulation.
 
I have never used one, but you do get back boxes that claim both fire & sound properties:
[automerge]1587389525[/automerge]

Not sure about how you get the cables in though, for best sound proofing you might need to seal it to the material, or use one of the glands that take T&E, etc.
[automerge]1587390215[/automerge]
Some glands claim to be LSF so presumably also a degree of fire retardant behaviour:
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

DaveW4

Trainee
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Student Level 3

Thread Information

Title
Wiring in soundproofing.
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
DaveW4,
Last reply from
DaveW4,
Replies
18
Views
3,438

Advert

Back
Top