Have been called to what could have been a very bad situation.

Home owner has started decorating and come across half a nail stuck in wall. It had been there for years and had penetrated cables going to a socket which were running slightly out of correct zoning.

I’ve recommended chasing the wall correctly and rerouting cables.

They’ve asked if there is an option which would cause less damage. In which case if I sunk a single box to house the repair with a blanking plate would this be acceptable. It would mean the junction is accessible and would bring the cables within the new zone.

I’d rather do the former but want to be flexible for customer whilst still sticking within regs.
 
Thanks.

Aswell as that is the circuit in question is not RCD protected. I’ve reconnended a board upgrade but would swapping out the breaker for an RCBO be a adequate temporary solution whilst they decide?

I think the owner was very lucky considering
 
Thanks.

Aswell as that is the circuit in question is not RCD protected. I’ve reconnended a board upgrade but would swapping out the breaker for an RCBO be a adequate temporary solution whilst they decide?

I think the owner was very lucky considering
Why does it need a board change? Will an RCBO fit in the existing board? And if it does, rather than a board change why not fit RCBO's where necessary?
 
They are doing a lot of renovations and were asking my thoughts on their current installation. It’s an old plastic cased board.

I suggested a modern metal board would be nice but can make current board more protected.

I’ll go with some RCBO’s initially
 
Sparks appear to be the only ones aware of such zones, or so it would seem.
Slightly off topic - having put a large hole through a wall to run my cabling back to the new board in a re-furb, I was a bit peed off to find on my return the plumber has also used the same hole with his push fit pipes touching my cables.
As for building regs and the drilling joists, again, plumbers just seem to drill and slot wherever it suits them best.
 
Sparks appear to be the only ones aware of such zones, or so it would seem.
Slightly off topic - having put a large hole through a wall to run my cabling back to the new board in a re-furb, I was a bit peed off to find on my return the plumber has also used the same hole with his push fit pipes touching my cables.
As for building regs and the drilling joists, again, plumbers just seem to drill and slot wherever it suits them best.
I remember from my days doing new houses keeping in zones and seeing the plumber run their pipes to rads etc not in any line/zone to them.
 
No they don't
As far as zoning is concerned,until other trades and the general public are aware of their existence, its almost a complete waste of time as far as they are concerned
Its a good idea having zoning if only all were involved
That really surprises me,its such a simple thing to do,if they ain’t getting that right,pity the other bits & pieces.
 
The only 'zone' I'll never use is the horizontal one at high level where wall meets ceiling, I just think that's asking for trouble in the future.
 
Op, could you elaborate on how the cable is not in a safe zone...is it running diagonally etc?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cheshunt

Thread Information

Title
Wiring slightly out of zones
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
17

Thread Tags

Advert

Thread statistics

Created
Chrisknowlesuk,
Last reply from
elsparko,
Replies
17
Views
2,739

Advert

Back
Top