Discuss max zs table in the osg in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
3
Hi all sorry for this silly question but i cant seem to find the max Zs table for a 10A BS88-2 Fusein the osg. I can find it in the BGB table 41.4
10A = 7.19 ohms and i know to multiply it by 0.8 (7.19 x 0.8 = 5.75) for rule of thumb but i would like to find the right table in the osg
 
Hi all sorry for this silly question but i cant seem to find the max Zs table for a 10A BS88-2 Fusein the osg. I can find it in the BGB table 41.4
10A = 7.19 ohms and i know to multiply it by 0.8 (7.19 x 0.8 = 5.75) for rule of thumb but i would like to find the right table in the osg
Page 122 ???? I think thats right
 
yellow? i'm still on the red one. it's the same electricity whatever osg you use.
 
Use the value in the reqs but don't forget to apply the 80% factor

To be honest, i've never used this 80% factor and probably never will now!!
Can't see the point of why they need to mess around with proven values that have served electrical installations well for literary donkey's years...
 
To be honest, i've never used this 80% factor and probably never will now!!
Can't see the point of why they need to mess around with proven values that have served electrical installations well for literary donkey's years...
i know your not in Britain, but if you were, surely you'd have to work to BS7671 requirements?

wouldn't not meeting these requirements constitute a C2
 
Last edited by a moderator:
the figures are given in BS7671 without the 80% correction factor. these are what i use. in winter when we are measuring @3 deg.C, not 20, should we then apply another correction?
 
i know your not in Britain, but if you were, surely you'd have to work to BS7671 requirements?

wouldn't not meeting these requirements constitute a C2

A C2 would be the code applied to a potentially dangerous fault found on an EICR, there is no such thing on an EIC.
If he has used values other than those in the books and recorded this deviation as part of the installations documentation then as long as the testing proves that the circuit is within those values there is no problem. Bs7671 is not the be all and end all of electrical installation!
 
Perhaps i should of also pointed out that the typical Zs values measured on our projects will meet and exceed anything that's presently deemed as max Zs values...
 
A C2 would be the code applied to a potentially dangerous fault found on an EICR, there is no such thing on an EIC.
If he has used values other than those in the books and recorded this deviation as part of the installations documentation then as long as the testing proves that the circuit is within those values there is no problem. Bs7671 is not the be all and end all of electrical installation!
doesn't an earth loop impedance value greater than that required warrant a potentially dangerous fault, ergo C2?

which other values apart from the manufactures are there?
 

Reply to max zs table in the osg in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top