Currently reading:
max zs table in the osg
Discuss max zs table in the osg in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all sorry for this silly question but i cant seem to find the max Zs table for a 10A BS88-2 Fusein the osg. I can find it in the BGB table 41.4
10A = 7.19 ohms and i know to multiply it by 0.8 (7.19 x 0.8 = 5.75) for rule of thumb but i would like to find the right table in the osg
Page 122 ???? I think thats right
yellow? i'm still on the red one. it's the same electricity whatever osg you use.
Use the value in the reqs but don't forget to apply the 80% factor
To be honest, i've never used this 80% factor and probably never will now!!
Can't see the point of why they need to mess around with proven values that have served electrical installations well for literary donkey's years...
i know your not in Britain, but if you were, surely you'd have to work to BS7671 requirements?
wouldn't not meeting these requirements constitute a C2
the figures are given in BS7671 without the 80% correction factor. these are what i use. in winter when we are measuring @3 deg.C, not 20, should we then apply another correction?
A C2 would be the code applied to a potentially dangerous fault found on an EICR, there is no such thing on an EIC.
If he has used values other than those in the books and recorded this deviation as part of the installations documentation then as long as the testing proves that the circuit is within those values there is no problem. Bs7671 is not the be all and end all of electrical installation!
Perhaps i should of also pointed out that the typical Zs values measured on our projects will meet and exceed anything that's presently deemed as max Zs values...
doesn't an earth loop impedance value greater than that required warrant a potentially dangerous fault, ergo C2?
which other values apart from the manufactures are there?
Been absolutely fine for god knows how many years, so what's suddenly changed to make previously stated accepted values now ''Potentially Dangerous''?? Answer '' ...NOTHING!!
don't quite follow u eng, nothings changed! just saying that exceeding max zs values as given in BS7671 is a C2 is it not? or is it all FINE!!!!!!
and just to muddy the waters further, manufacturers data could well give a higher figure. as long as the MCB/fuse will operate within the specified time, then bob's your dad's brother.
so, you work out your fault current which is dependant upon impedance (Zs) then look up the time characteristics data for disconnection time.
Electrical Installation Certificate EIC
the time/current graphs in BS7671 are generic. different makes of OCPDs may well give different (better) figures.
Think about it for a second, previously stated max Zs values satisfied ADS requirements, so how can you, (or should i say they) now say that they Don't??
Of all the things that needed sorting out within BS7671, max Zs values wasn't and still isn't one of them. A totally wasted Amendment opportunity all round, when you also take into account the plastic/metal CU farce!!!
Reply to max zs table in the osg in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net