First of all hello, this is my first post. Did try a search to answer my question but was unsuccessful.

I am connecting the AC side of a PV solar installation. im not an out and out electrician but I am qualified for the purpose of my job as a maintenance engineer.

Baisically my question is, how do i connect to the existing circuits within the CU? Do they go straight onto the main incomings? (with a breaker inbetween)
A friend I'm doing it for wants it to just power his lights, as the panels he's got are not enough to power the whole house.

This may be a simple answer! But just want to check
 
Are you MCS registered and part of a competent persons scheme?

you can't just go connecting to the grid without informing the DNO. Is the system G83 compliant? As this is a new circuit it's also notifiable!
have you checked for bonding etc?
 
Last edited by a moderator:
im not connecting to the grid. Using a manual switch at the moment. At no point will the solar output be connected to the mains.
im just curious as to how it is physically wired up on a 'normal' installation
 
First of all hello, this is my first post. Did try a search to answer my question but was unsuccessful.

I am connecting the AC side of a PV solar installation. im not an out and out electrician but I am qualified for the purpose of my job as a maintenance engineer.

Baisically my question is, how do i connect to the existing circuits within the CU? Do they go straight onto the main incomings? (with a breaker inbetween)
A friend I'm doing it for wants it to just power his lights, as the panels he's got are not enough to power the whole house.

This may be a simple answer! But just want to check

don't connect into a shared RCD. Other than that, if you're competent then you should be able to work it out.
 
Right so it should be connected before the main double pole breaker?
i take it the 'house' would take the power from the path of least resistance, so when voltage from solar drops it'll automaticly draw it from the mains?
and I take it the inverter has got to be pure sine wave
 
i take it the 'house' would take the power from the path of least resistance, so when voltage from solar drops it'll automaticly draw it from the mains?

If you are doing this then the system IS connected in parallel to the grid and you DO need to comply with G83 (including using a G83 certified inverter) and inform the DNO.
 
Last edited by a moderator:
It is wired seperatly from the mains and using a DPDT switch to switch between the two sources.
 
I'm not doing that. It's off the grid and will manually transfer between mains and solar using a DPDT switch.
So the solar installation can go straight onto the incomers even if it isn't powerful enough to power the whole house?
 
so. he wants to power his lights from solar in the daytime when he doesn't need the lights, but when he needs the lights, it will be dark and the solar panels will just be sitting there waiting for dawn? sounds to me like a half-baked crackpot idea. is he an architect, by any chance.
 
so. he wants to power his lights from solar in the daytime when he doesn't need the lights, but when he needs the lights, it will be dark and the solar panels will just be sitting there waiting for dawn? sounds to me like a half-baked crackpot idea. is he an architect, by any chance.
your right tell the client is a fool.

one way to do it would be charge batteries then run the lights off the batteries (bassically a homemade ups, has the added benerfit of no loss of lights during changeover etc)
 