You can't issue a coded observation based on "It hasn't got what you usually see a lot of" though can you ?
yes i understand that . I just thought this was a requirement to have some sort of isolation point local to the heaters?
You can't issued a coded observation based on what you suspect may be required either.
thats why im on here andy to get some guidance and advice.
What code if any would you be inclinded to give a DB that isnt in a cupboard or within any barrier, ect.
I mentioned this in post 7 " it would depend on the environment for barriers around service Head , for example if fork lift truck could hit it then I would agree with a code 2" every installation is different so there is not just one answer to this
My best guidance and advice would be that if you are not sure whether something is required by the regs or not then look it up in the regs. It's going to take a long time to go through all your original points at this rate.
A lot of your original points would be dependant on the situation and it would be impossible to tell you what code as some could range from no code to a C2 dependant on other factors. It's down to the inspector to deem issues dangerous or not based on the situation, but all observations must have a basis in the regs otherwise it's not a technical report based on the requirements of BS7671, it's just opinion.
If you could answer all my points in red from my first post then we could start from there.
I would also advise some serious revising or studying as you seem to be picking codes at random without any thought or justification as to why. If a client handed me an EICR with all your points coded as they are in your original post I would tell them that someone either didn't know what they were doing, and/or is trying to pull a fast one with a large remedial works bill.
I'm not trying to be harsh with that comment, just offer my truthful opinion.
1. No fuse spur to heater (hard wired straight to MCB with correct size cable and MCB for heater)- Im thinking code 2?
This isnt an issue as the MCB can be used as local isolation (not best practice but not against regs)
2. No isolator/fuse spur to curtain heater (hard wired straight to MCB with correct size MCB and cable for curtain heater in question) - again code 2?This isnt an issue as the MCB can be used as local isolation (not best practice but not against regs)
3. Missing lid that covers MCBs (not fuse board cover) Code 3? Does this impair the IP rating of the enclosure? If not then no issue.
4. Different manufacture MCBs in board. (e.g 12 way wylex board with 11 wylex MCBs and 1 hager MCB) code 3? I would agree with C3 for this, Regs states follow Manufacturers info, Manufacturers info says use their products only
5. Cables not supported in their runs? code 2 C3
6. Cables not supported above false ceiling and lying on metal frame work. C3
7. Emergency lights not wired correctly for testing - just info Explain what you mean
8. Main service incomer in open with no cupboard or barrier - code 2 with recommendation of some sort of cupboard or barrier.
No Issue as long as relevant IP rating have been adhered to
9. DB in open with no cupboard or barrier - code 2 with recommendation of some sort of cupboard or barrier added to cover No Issue as long as relevant IP rating have been adhered to
10. No visable signs of supplementary bonding - If it looks like it could be covered in building fabric and able to obtain a very low resistance reading with a wander lead then - info with notes Read requirements for omition of Supplementary bonding in section 701, confirm by applying reg 415.2.2
11. Breakers such as 3871? code 3 recommend upgrade to 60898 breaker Unless their breaking capacity has been exceeded no issue
12. Old board with 3871 breakers with half upgraded to 60898 breakers - code 2 with recommend the rest upgrade to 60898s potentially a C3 unless same manufacturers equipment used.
13. Fire panel not wired from DB to fire panel in fire resistant wiring - code 2.
14. No main switch between incomer and DB or first DB - code 2 if commercial No requirement
15. RCD as main switch on DB - code 2 with recommendation of main switch added even if it means a board change a no spare ways C3 as there is no division of the installation, although no spare ways doesnt mean a CU change necessarily.
These are my opinions on the coding.
if anyone would like to add to this list it may be helpful for others including myself.
13. Fire panel not wired from DB to fire panel in fire resistant wiring - code 2. This is not a BS 7671 Reg But is in the fire alarm regs BS 5839-1:2013 so I would give it a code 3
I agree that it is BS 5839-1:2013, but this does not mean that a C3 coding is appropriate. It means that it must not be coded as it is not a non-compliance with BS 7671:2008 (2015). As such a covering letter would be perhaps the best place to highlight the issue - but certainly not in an Electrical Installation Condition Report to BS 7671.
I would say that fire alarm supplies are covered by BS7671 and are required to be fire resistant.
560.5.2 and 560.8.1
Indeed. What I was getting at was not that it isn't non-compliant with BS 7671, but that if you are claiming non-compliance with another Standard then the EICR isn't the place for that observation. It may come under the Regulations for safety circuits in BS 7671 if I look into that later - and if so would be notable in the EICR.
I came across one today that had me slightly stumped.
1mm T+E from socket on ring final, to feed some lighting via a 3A fuse in a SFCU.
It seems wrong to do this and I never would, but theres no way the cable from the socket to the SFCU can be overloaded as the 3A fuse obviously limits current flow in that cable.
Thoughts? Struggling to think of a reg this contravenes...
524.1 referencing table 52.3 Minimum size for power circuits is 1.5mm
If the cable from the socket before the fuse is 1mm² then this is power wiring and the minimum size is now 1.5mm², but really it will not be a problem and could be considered as the spur is for lighting only, perhaps.
Hi guys,
just looking for some advice on a few common issues ive found when conduction a commercial EICR and how best code them. Any advice and help is much appreicated.
So hear are some the senarios
6. Cables not supported above false ceiling and lying on metal frame work. code 2?
9. DB in open with no cupboard or barrier - code 2 with recommendation of some sort of cupboard or barrier added to cover DB.
11. Breakers such as 3871? code 3 recommend upgrade to 60898 breakers
12. Old board with 3871 breakers with half upgraded to 60898 breakers - code 2 with recommend the rest upgrade to 60898s.
1, 2, 3, 4, 5, 7, 8, 9, 11, 12, 14, 15 sound like no codes to me based on the limited info you have given.
Remember code 2 is only for situations where a potential danger exists. Unless you can specify exactly what the potential danger is and a regulation to support it then don't code it.
paulthemagpie,
davesparks,