So the fact Table 52.3 states that the minimum size for power circuits is 1.5mm2 doesn't mean using 1mm2 goes against the regs? If it does, surely it needs coding?

No, you are not assessing absolute compliance with 7671. You are assessing the installation's suitability for continued service using 7671 as the reference for the standard of safety. You do not code things just because they are 'against regs', solid green earths, old core colours and imperial cable sizes are all arguably 'against regs' but you don't code them as they have no effect on safety.
C3 is to be used to code observations where an improvement could be made for safety, it is not for identifying items which could be changed just for the sake of satisfying a regulation.
If the 1mm is operating safely as it is then there is no observation to made.
If the 1mm is undersized for the load or fault current then it would be a C2 as it would become dangerous under fault conditions.
 

Reply to EICR codes advice in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Hi - we have an inline heater for a vent system that appears to always be on. I believe the electrician may have wired it incorrectly with only a...
Replies
3
Views
705
Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
280
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
680

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock