Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb.
I know this is bad practice to install unless using bigger SWA to achieve required csa's in awkward spaces to terminiate.

My question is what code is this? Im going with C3 with recommendation to rectify, but there is an inadvertent danger if 1 leg had a loose termination or worse was removed causing remaining leg to bear the load while being protected by an over rated mcb.

Any help greatly appreciated.

Smarky
Smarky
 
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb.
I know this is bad practice to install unless using bigger SWA to achieve required csa's in awkward spaces to terminiate.

My question is what code is this? Im going with C3 with recommendation to rectify, but there is an inadvertent danger if 1 leg had a loose termination or worse was removed causing remaining leg to bear the load while being protected by an over rated mcb.

Any help greatly appreciated.

Smarky
Smarky

Are both runs exactly the same length and routing?
 
Are both runs exactly the same length and routing?
Hey DPG, thanks for chiming in.
Yes they are the same runs.

Thanks
 
  • Like
Reactions: DPG
  • Like
Reactions: DPG
Ok Thanks so much for your input!!

No worries. I was going to type something more in depth but I decided to sit in the garden with a beer. I've coded that C3, because two beers will be an improvement.
 
No worries. I was going to type something more in depth but I decided to sit in the garden with a beer. I've coded that C3, because two beers will be an improvement.
Im about to do exactly the same and open a couple myself, Its nice and sunny where I am, enjoy!!!!!
 
  • Winner
Reactions: DPG
Parallel cables Are ok as a general rule.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What code for this EICR if any
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Thread Tags

Tags Tags
code eicr

Advert

Thread statistics

Created
Smarky,
Last reply from
Dustydazzler,
Replies
8
Views
1,401

Advert