I would treat it like any other DB
List the supply characteristics, incoming fuse type and rating etc.

It is in many ways similar to a caravan or temporary building.
Fixed wiring and distribution, fed from a socket that is part of a larger installation
I agree with James.

I understand also why some might say to ignore it, because it's not part of the fixed wiring. But neither is this just an extension lead being used for normal purposes. There is a consumer unit fed from it. This consumer unit and its final circuits are items of fixed wiring and so should be treated accordingly in my view.

If the inspector chooses not to view it as such, then surely it should be included in the extent and limitations, at least.
 
It isn't part of the fixed electrical installation.

Correct it technically is not, but the fact it was put in like this shows me it should be and surely should be my responsibility to highlight?

I agree with James.

I understand also why some might say to ignore it, because it's not part of the fixed wiring. But neither is this just an extension lead being used for normal purposes. There is a consumer unit fed from it. This consumer unit and its final circuits are items of fixed wiring and so should be treated accordingly in my view.

If the inspector chooses not to view it as such, then surely it should be included in the extent and limitations, at least.

My thoughts exactly.

So can anybody see an electrical safety reason as to get rid of the plug top and instead extend the the 4mm radial (which already supplies 3 sockets) to supply the sub board?
 
I agree with James.

I understand also why some might say to ignore it, because it's not part of the fixed wiring. But neither is this just an extension lead being used for normal purposes. There is a consumer unit fed from it. This consumer unit and its final circuits are items of fixed wiring and so should be treated accordingly in my view.

If the inspector chooses not to view it as such, then surely it should be included in the extent and limitations, at least.
And to add if that CU was ever changed it would be a notifiable job too. lol
 
Of course you can mention it but you will have difficulty putting a Regulation against it as it is outside the scope of BS7671.
 
Got to admit this is a tricky one.

ive done loads of EICRS where there are numerous extension leads.

I always put in comment.
Excess number of extension leads in property possibly due to insufficient number of sockets. This EICR does not include testing of these extension leads and All testing done with them unplugged. C3 potential for over load If extensions are all in use.

this one is different. A CU from a plug Feeding numerous circuits.

I think the bigger question is test or not to test.

me. To cover my arse. I’d say don’t test and state that in extent installation tested.
 
Very interesting thread... it may have highlighted a glaring big hole in the regs !

IMHO... if I was doing the EICR... I would have to mention it somewhere, simply ignoring it would not be an option. If there was no evidence of overheating/damage and it was correctly fused with a proper fuse (not some obvious Chinese fake), I'd give it a C3... I can see the arguments for ignoring it though.
 
Just had a though. Because it’s on a plug top and bottom would a PAT tester be needed? or would they say it’s not in there remit?
if it is in there remit do they test the plug only?
if they do test the plug only,
Who tests the circuits and board?
not us as it’s not part of the hard wired installation.

lots of questions no answer.
 
I’d like to thank all who have participated, it’s been very interesting/enlightening!

Ive decided to acknowledge the presence of it on the EICR and to recommend that the supply is upgraded, but to say the sub board has not been tested due to it not being part of the fixed installation.

It’s then down to the customer what they do with it!
re-jig the feed to the sub from it's own dedicated MCB. (6mm cable on a 40A. RCD protected??). but that's not in your remit of doing a EICR. quote it.

That would be the way to do it, unfortunately that would mean running a new cable across a newly decorated place with new flooring! Either very unsightly or very costly.
 
I'd say that your responsibility ends at the socket. Check that for heat damage, and if OK, that's it.
Certainly make written comments attached to the EICR, but they won't be actually part of the EICR.
I have a caravan outside which is permanently connected to a 13A s//socket, when it's not on its jaunts around Europe. Would you include the wiring of the caravan in a EICR of my property?
How about if there was a 100A s/fuse right beside and connected to the DNO supply of a 4 bed house, the s/fuse feeding a 125A blue socket, with a matching plug feeding the CU? House wiring except from part P?
 
Something doesn’t seem right with me classing it as only a C3 either!

The loading of the air conditioning unit shouldn’t matter should it? If it pulls more than 13A the plug top would blow.

My concern is the 1.5mm flex cable that is on the plug top could overheat if too much current is drawn .. but the fuse would operate if there was any danger? Or am I wrong in assuming the 1363 fuse is adequate?
If this was to be treated as part of the fixed wiring, then I believe (though stand to be corrected) that a 13A BS1362 fuse will protect a cable rated at =>18A.

433.1.1 and 433.1.201 are relevant , in particular:
433.1.1 (iii)
The current (I2) causing effective operation of the protective device does not exceed 1.45 times the lowest of the current-carrying capacities (lz) of any of the conductors of the circuit.

In the case of a 13A BS1362 fuse, I2 is ~ 26A, or 2 times 13A.

13 X (2/1.45) = 17.9A
 

Reply to Sub Board fed from a plug top, EICR Coding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
697
hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
734

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock